Anonymous Poster #1

Metal Halide Lamp on Uninterrupted Power Supply

11/07/2012 9:06 AM

Hi,

I just need to know please if it's possible to feed a Metal Halide through an Uninterrupted Power Supply (UPS). I have never seen something like this in the design. Can you tell me why pls?

thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#1

Re: Metal Halide Lamp on Uninterrupted Power Supply

11/07/2012 9:17 AM

I'm certain that some UPS can easily drive a Metal Halide lamp. I'm equally certain that some UPS cannot drive any of these types of lamps.

I flipped a coin and it tells me that you cannot do this with your supply and lamp.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Metal Halide Lamp on Uninterrupted Power Supply

11/07/2012 9:35 AM

It depends rather a lot upon the rating of the UPS and the rating of the lamp, neither of which have been shared with the forum.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Metal Halide Lamp on Uninterrupted Power Supply

11/07/2012 10:18 AM

You guys and your negative waves.

Sure you can drive a MH lamp with a UPS.

Next question?

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#4
In reply to #3

Re: Metal Halide Lamp on Uninterrupted Power Supply

11/07/2012 11:54 AM

I guess I should have used another coin.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Metal Halide Lamp on Uninterrupted Power Supply

11/07/2012 3:33 PM

Another p** grower trying to save his crop after a power loss eh?

With enough money, you could connect whatever you like behind a UPS. But as the size goes up and/or the type of load gets more demanding, the cost of the UPS goes up exponentially. I once did a system for military temporary radar stations where they wanted to be able to hold up a small air conditioner for the building for 3 hours in order for them to have time to get fuel for the backup generator if necessary. It took a 25kVA UPS system to run a 2HP AC unit for that long and ensure that the starting surge for the motor would not shut it down towards the end of the battery life. So it cost them about $30K at that time to be able to accomplish this.

I hope you get a good price for that crop...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#6
In reply to #5

Re: Metal Halide Lamp on Uninterrupted Power Supply

11/07/2012 10:52 PM

Tsk, Tsk, a suspicious and inventive mind.

Metal halide light is a gas discharge tube at its most basic. It has strange nonlinear I vs. V (current vs. voltage) characteristic, Including negative resistance portion of it. Using it straight as a load is an excellent way to kill the power source (that was built for resistive and inductive loads), and at the same time to blow the light bulb too. It takes some solid engineering to match such a misbehaving load to a conventional source.

On a second thought Raef might be right.

Reply
Power-User

Join Date: Nov 2011
Posts: 258
Good Answers: 2
#7

Re: Metal Halide Lamp on Uninterrupted Power Supply

11/07/2012 11:44 PM

Metal Halide lamp has peculiar characteristics. Its body temperature is nearly 40 Deg C or more while in operation. When there is a short power fail of the order of even 0.1 sec, the lamp turns off and unless body temp is down to nearly 150 Deg C or lower it does not light up again- though you have UPS back restoring power even in milisec after say 0.1 sec of power fail. Lamp cooling is dependent on ambient conditions, luminaire design etc etc. It may take 10 to 15 minutes or longer depending on indoor, out door, season etc etc. This is the answer to your question.

To light up a MH lamp one generally applies about 2.5 to 3 KV sharp pulse (pulse width etc- I will not discuss here) - which is generated by teh igniter in combination with normal choke/ ballast.

However I had design, demonstrated and made a metal halide lamp to turn on within about 6 to 8 seconds after a brief power fail like this using specially designed choke and specially designed igniter. So there is a solution too- which is expensive and not commercialized widely - for unknown reasons. I had demonstrated this to reputed lighting companies in India. Hence in case of emergencies, people do install other types of lamps to light up during such 10 to 15 minute breaks.

Reply
Guru
Australia - Member - New Member Fans of Old Computers - H316 - New Member Hobbies - Model Rocketry - New Member

Join Date: Jun 2006
Location: Port Noarlunga, South Australia, AUSTRALIA (South of Adelaide)
Posts: 3048
Good Answers: 75
#8
In reply to #7

Re: Metal Halide Lamp on Uninterrupted Power Supply

11/08/2012 3:45 AM

"When there is a short power fail of the order of even 0.1 sec, the lamp turns off"

If you have a decent Uninterruptable Power Supply that is worthy of its name then that's what you get and uninterrupted power supply that doesn't change when the mains power fails. As far as the load is concerned when the mains power fails nothing has happened and it carries on exactly as it was prior to the mains failure.

Unfortunately there are a lot of cheap and nasty UPSs on the market that either don't supply a proper sinusoidal output or have a change in the output voltage when the mains fails.

So the moral of the story is to stick with a reputable manufacturer that is known to produce reliable UPSs that do what their name states and supply you with uninterrupted power.

You will also need to check with the UPS manufacturer or supplier that the unit you are selecting is capable of handling the start-up power requirements of your specific load which in this case is metal halide lamps.

__________________
An elephant is a mouse built to government specifications.
Reply
Guru
Hobbies - Musician - New Member Hobbies - Car Customizing - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2007
Location: FL Space Coast
Posts: 536
Good Answers: 14
#9

Re: Metal Halide Lamp on Uninterrupted Power Supply

11/08/2012 7:17 AM

One thing I would make sure of is that the UPS puts out a true sine wave. Most of the inexpensive UPS's put out a single step modified sine wave. Basically a reduced voltage square wave with a certain amount of dead time between pulses. I don't think that the lamp or, more specifically, it's ballast will work very well on a modified sine wave.

Reply
Power-User

Join Date: Nov 2011
Posts: 258
Good Answers: 2
#10

Re: Metal Halide Lamp on Uninterrupted Power Supply

11/08/2012 8:19 AM

One needs to be practical. I am not sure of end application fro MH being connected on UPS. Let me give you an example of a huge MALL or Parking lot or street light or tunnel lighting. The power requirements are so huge- no break UNINTERRUPTIBLE UPS is not practical and not economical. Hence for tunnel lighting in fact MH lamps are NOT USED at all. In huge malls, diesel generator comes on - but may take a few minutes- during which MH will not light up and will remain off for 10 to 15 minutes, and alternate back up lighting is provided. Another example is day and night cricket matches - which have become now-a days - are played with entirely diesel generator supply to avoid a short break in supply. You can imagine costs involved and even matches can be lost, if there is a short break. You are welcome to look at many sports applications, indoor stadiums and other huge complexes- where such no-break uninterruptible supplies are installed. For one or two 70 w or 150 w lamps it is oK.

CR$ administrators- kindly see spell check is NOT WORKING.

Reply
Guru
Australia - Member - New Member Fans of Old Computers - H316 - New Member Hobbies - Model Rocketry - New Member

Join Date: Jun 2006
Location: Port Noarlunga, South Australia, AUSTRALIA (South of Adelaide)
Posts: 3048
Good Answers: 75
#12
In reply to #10

Re: Metal Halide Lamp on Uninterrupted Power Supply

11/09/2012 8:14 AM

"The power requirements are so huge- no break UNINTERRUPTIBLE UPS is not practical and not economical."

The cost is always a factor that needs to be taken into account but the original poster asked about the use of an UPS and it should be noted that I said:

"If you have a decent Uninterruptable Power Supply that is worthy of its name"

In your situation you are talking of a Backup Power Supply that comes on line sometime after the mains power has failed not an UPS.

However as vargaalex stated in his post one solution is to have small UPS units built into each light fitting that keep the power supplied to the light when the mains fails. That way you don't have to worry about the huge inrush currents and problems associated with starting the light because it will always be started when the mains power is available, all the UPS has to do is supply an appropriate voltage and current to maintain the lights operation. It also means that you don't have to worry about one huge battery bank and a similarly large inverter that supplies the AC power to the lighting system and must be capable of handling the start-up power requirements. You are also not putting all your eggs in one basket so that in the event of an UPS malfunction you only lose one light not all of them.

__________________
An elephant is a mouse built to government specifications.
Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#11

Re: Metal Halide Lamp on Uninterrupted Power Supply

11/08/2012 9:30 AM

Most any lights can be powered from a UPS, and those used in some installations for emergency lighting are connected to a UPS.

The real issue is sizing the UPS to handle all the loads connected.

Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#13

Re: Metal Halide Lamp on Uninterrupted Power Supply

11/09/2012 10:27 AM

Hallo XYZ, Masu, Varga

I worked in and for telecomm. center most of my life. By necessity, We had always on power supplies. That is the most expensive, most maintenance demanding, absolutely best kind. It is the power thru all the time architecture. Rectifier, battery, DC/AC all the time. Most people and outfits cannot explain the expense, and opt for cheaper alternative. Most of which cuts in asynchronously (with consequences), and usually supports operation, until operation can be shut down in an orderly fashion.

Mostly it is a promise, not fulfilled, with consequences. Fingerpointing follows.

Then history repeats.

Reply
Power-User

Join Date: Nov 2011
Posts: 258
Good Answers: 2
#14
In reply to #13

Re: Metal Halide Lamp on Uninterrupted Power Supply

11/10/2012 2:16 AM

Thanks- I like your pointing out ground realities in the field. For telecom exchanges - you need un interruptible supplies. When it comes to a huge shopping mall with say 200 to 300 or sometimes even 500 light points- each fitted with smallest 70w (not 150w) Metal Halide lamps -it is not easy or economical to provide no break power supply.

Reply
Guru
Australia - Member - New Member Fans of Old Computers - H316 - New Member Hobbies - Model Rocketry - New Member

Join Date: Jun 2006
Location: Port Noarlunga, South Australia, AUSTRALIA (South of Adelaide)
Posts: 3048
Good Answers: 75
#15
In reply to #14

Re: Metal Halide Lamp on Uninterrupted Power Supply

11/10/2012 5:38 AM

"When it comes to a huge shopping mall with say 200 to 300 or sometimes even 500 light points- each fitted with smallest 70w (not 150w) Metal Halide lamps -it is not easy or economical to provide no break power supply."

I agree wholeheartedly and this is probably the reason that the original poster has never seen it done. In such situations there are far more economic solutions like self‑contained emergency lighting systems that only come on when the mains power fails.

However, the original poster asked if it was possible to power a metal halide lamp with an UPS which is technically possible given a unit that is of sufficient quality and capacity. Whether or not it's economic or practical is a completely different question.

__________________
An elephant is a mouse built to government specifications.
Reply
Reply to Forum Thread 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

IanR (1); JRaef (1); leveles (2); lyn (1); masu (3); PWSlack (1); redfred (2); vargaalex (1); xyz (3)

Previous in Forum: Urgent-Abt Busbar Sizing Calculation   Next in Forum: High Voltage Test

Advertisement