Phase Nullify in the Electric Bus

11/09/2012 2:31 PM

When one of the three pases are checked, found R phse is not indicating in the tester.How ever voltage across is as usual.Volatage between R phsae and ground is 415v(In this case line voltage),Upon checking it was observed that welding transfer feeder is faulty.Please clarify why bus not tripped on earth fault and why this happens?please clarify............................

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: Nov 2012
Posts: 4
#1

Re: Phase Nullify in the Electric Bus

11/09/2012 2:53 PM

IS the neutral for the system grounded.If not then it may be a case of arcing ground as voltage has risen from phase voltage to line voltage between phase and ground.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#2

Re: Phase Nullify in the Electric Bus

11/10/2012 7:37 AM

Maybe it's the way your voltmeter is connected into the circuit. If you're connecting one lead to the R phase instead of Neutral or Ground, you will read what you are reading.

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#3

Re: Phase Nullify in the Electric Bus

11/10/2012 10:27 PM

Uppalsn,

In some industrial settings the circuits are intentionally not referenced to ground (or earth). These are called "ungrounded delta" in the USA. The purpose is so that any accidental ground in the equipment does not cause a fault trip of the protective device and loss of power to the equipment or process. In these cases, however, there should be a ground detector that would warn the maintenance workers when one phase became grounded. They could then locate and fix the problem without any loss of production. I have seen and worked with ungrounded delta systems operating at 480 and 2300VAC.

I suspect this is the type of circuit you have observed.

--JMM

Register to Reply