why there is no grading in surge arrester which is located in over head line?
and can any body tell me the types of surge arrester used to
protect the high voltage line?
Pathfinder Tags: Surge Arrester
Good Answers: 34
Re: Grading ring
11/10/2012 3:56 AM
What do you mean by "no grading in surge arrester"? Can you give some example?
Good Answers: 445
Re: Grading ring
11/10/2012 1:06 PM
It means that there is no grading ring in the surge arrester. A grading ring is used to distribute the electrostatic field near high voltage connections to ensure that the field gradient does not exceed approximately 30kV/cm, the breakdown voltage for air as an insulator. Above this corona may appear depending upon the ambient conditions.
The reason that there are no grading rings is probably because OP is looking at a 66kV class arrester whereas grading rings are usually found on equipment above 138kV, though in some cases conditions may warrant their use at a lower voltage.