Energy Meter Show Different Current on Different Phase

11/14/2012 9:47 AM

hello i have installed 3 phase ,4 wire energy meter having manufacture secure meter limited i have make the connection of the meter properly ,having connected on the 66 KV level having CT ratio 400/1 i have faced the problem is that on one phase (R phase) it show full current but on the other two phase it show very less current ie if on R phase it show 200 Amp. then on the other two phase it show 80 Amp. approximately please tell me where is the problem . one thing is that i have checked the Ct connection it found ok. please help me

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: energy meter show different current on different phase

11/14/2012 9:58 AM

The problem lies in the lack of vision and knowledge of single-phase electrical installers.

When adding single phase loads to an existing three-phase LV board, the electrician naturally starts from the top-left, which in most boards is the red phase. So the red phase is usually more heavily loaded than others, which is reflected in the high current in the red phase of the HV incomer.

Fortunately, the remedy is simple: slap the electrician round the head with a wet kipper until the excess of red single phase loads are redistributed more evenly across the three phases.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#2
In reply to #1

Re: energy meter show different current on different phase

11/14/2012 10:09 AM

"round the head with a wet kipper"???

Any kipper I ever ate would break before you could use it to slap anything. However, not being a Brit, I must surmise that maybe you folks have raw ones(??) although that defeats the definition of a kipper to me.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: energy meter show different current on different phase

11/14/2012 10:19 AM

It would make quite a mess, wouldn't it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Jun 2012
Posts: 11
#4
In reply to #1

Re: energy meter show different current on different phase

11/14/2012 10:25 AM

sir you cannot understand the question the energy meter is installed on 66 KV level in the grid station and the power is supply on the 66 KV level

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: energy meter show different current on different phase

11/14/2012 10:28 AM

So? Why is that relevant? All the single phase loads are on the LV side.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #5

Re: energy meter show different current on different phase

11/14/2012 10:41 AM

Perhaps the wet kipper should be applied to the OP and not the electrician?

Register to Reply Score 2 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #6

Re: energy meter show different current on different phase

11/14/2012 11:02 AM

Interesting thought.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#10
In reply to #6

Re: energy meter show different current on different phase

11/15/2012 2:23 AM

lyn, an off topic post has a score of 5 points when posted. Now your off topic score is 3. Does it mean that you have received 2 GA points? Dose that add to your overall GA figures?

Register to Reply Off Topic (Score 7)
2
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#7
In reply to #4

Re: energy meter show different current on different phase

11/14/2012 11:02 AM

Sir, it is obvious you do not understand the difference between voltage and current

...and one and three phases

...and power quality and efficiency

...and learning and...well, there is no comparison for learning.

Register to Reply Good Answer (Score 2)
Commentator

Join Date: Dec 2009
Posts: 87
Good Answers: 5
#11
In reply to #1

Re: energy meter show different current on different phase

11/15/2012 2:53 AM

OK my story runs on the LV side.

Two TV Transmitters were to be approved by customer and we were running the final tests. The last test for the approval report was the current draw on the three phase mains input of both identical transmitters. Transmitter A had on all three phases 200A each - as it was expected and verified several times before.

At transmitter B due to mechanical reasons we started to take measurements in reverse T= 200A S=200A but R phase showed something funny: 200A but jumped for 1 sec to 210A and then for 2 seconds back to 200A. Even the customers engineer was scratching his head. This change could not be explained as other measurements during the whole day it was always 200A.

Closer inspection showed that there was an unaccounted for, new wire connected to this R terminal. Investigation resulted in the fact that someone from the station personal had unnoticed connected the red warning lights of the antenna tower to this terminal. Fog had come up so the warning lights turned on..... the rythm was 1sec ON 2 sec OFF. Took us quite some time to figure this out as the lights were hundreds of meters above our heads.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#14
In reply to #11

Re: energy meter show different current on different phase

11/16/2012 11:44 AM

We had something similar on what were supposed to be known circuits. It turned out that the standby mode for a large copy machine included turning a heating circuit on and off in somewhat continuous patterns.

An extension cord and power strip under the raised floor was extended to a receptacle for the wrong panel.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9

Re: Energy Meter Show Different Current on Different Phase

11/14/2012 11:47 AM

Check to make sure your CTs are properly oriented.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#12

Re: Energy Meter Show Different Current on Different Phase

11/15/2012 6:06 AM

Dear sehdev singh,

You have stated that you have installed 3 phase, 4 wire energy meter on 66kV level. At this voltage level, generally, it is either star or delta connected, 3 phase 3 wire system, there is no connection of neutral to the load. Therefore where you have connected neutral(4th.terminal) terminal of the energy meter?. In general, 3 phase 4 wire energy meter(unbalanced type meter) is connected in LV 3 phase 4 wire electrical power distribution system where loads are unbalance ,neutral is connected to loads and total unbalace current is flowing thro' the neutral line; the neutral of the energy meter is connected with neutral. The circuit diagram with CT connections is supplied with the meter.Therefore, it requested to check your meter connection.

Regards,

Manindra.

__________________
Manindra
Register to Reply
Active Contributor

Join Date: Sep 2011
Posts: 14
Good Answers: 1
#13

Re: Energy Meter Show Different Current on Different Phase

11/15/2012 7:53 AM

Can you check the accuracy class of CT mismatch

Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

cuba_pete (2); GURUMOORTHY (1); Joshi (1); JRaef (1); lyn (1); manindra (1); Phys (1); PWSlack (4); sehdev singh (1); uli_newBuilder (1)

Previous in Forum: Electrical Wiring   Next in Forum: Direct Mount SSR / Heater Controller

Advertisement