Previous in Forum: Early Streamer Emission Air Terminal Rejection!   Next in Forum: Voltage Drop Analysis
12 comments
Choice of a Transformer For a Generator
11/18/2012 4:25 AM
Generator : 25/31.2 MW/MVA, 11 kV
Output voltage from generator is 11 kV. This power will be supplied at 132 kV i-e Voltage is step up from 11 kV to 132 kV through step up transformer. The transformers to be installed will either be
Transformer - 1: 31.5 MVA, 11/132 kV
Transformer - 2: 35 MVA, 11/132 kV
Which one is the best choice in these two transformer to be installed at the the out put of the Generator.
Good Answers: 34
Re: Choice of a Transformer for a Generator
11/18/2012 10:15 AM
11/18/2012 10:22 AM
Yes ,
Transformer -2 Looks more appropriate but any technical justification for Transformer - 2 (Like in transformer-1 may have probability of heating etc)
11/18/2012 10:39 AM
Transformer #1.
I have absolutely no technical basis for this choice, but there's a 50-50 chance that I will be right.
What do the suppliers say? They probably have some real engineers on staff who may be able to make informed decisions.
You could always flip a coin.
11/18/2012 11:01 AM
One supplier suggest Transformer-1 while other suggest Transformer-2. Seeking for best Choice ...........Some pros and cons about both choices
11/18/2012 11:15 AM
Seek a third opinion from a real engineer who can understand what is required of the transformer.
You have provided no information about what it is supposed to do.
Re: Choice of a Transformer For a Generator
11/19/2012 1:19 AM
if the price is the same and other specifications are the same then transformer 2 is the best option. @ least you have reserve capacity.
11/19/2012 3:11 AM
Assuming you'll run at 25/31.2 MW/MVA all the time, consider these aspects:
-the efficiency of a transformer starts to drop when the load increases over about 75%. In the end this is wasted energy.
-the external fault current can be another aspect to look for when choosing the transformer. There is one thing to have a high current spike with transformer loaded close to 100% and another one with 75-80% load. (a couple of kA is a lot of current even for just 0.5 seconds and your transformer will have to handle it)
The time is ......now
11/19/2012 4:48 AM
From your generators capacity (25/31.2) you have only one choise which is option -1 (31.5 MVA)
11/19/2012 7:34 AM
How and Why we have only one option of choosing only 31.5 MVA transformer
Good Answers: 445
11/19/2012 9:22 AM
What answer did you give and why?
In reality you cannot choose based upon the limited information that you been have provided. You need to know such things as cost, impedance, if the transformer is rated for generator duty (short circuit withstand capability), whether there are taps, winding configuration, where the transformer is in the system (isolated, end of line, grid, etc.), the expected operating point of the generator (generators are rarely operated exactly at their nameplate), etc., etc. The interviewer was trying to determine how much experience you have in this field.
02/12/2013 11:07 AM
Dear Mr.Salar,
The tendency is to decide on the Higher Capacity of the Transformer. But several Factors are to be taken in to consideration - like No-Load Losses,
I^2 R losses in the windings at full load, over-all efficiency, Life for Insulation, i.e., Estimated Life of Insulation as per "ARRHENIUS LAW" is to be evaluated.
The "ARRHENIUS LAW" is given as V = 10^(a+b)/T,
where V is the Estimated Life Expectancy for the Insulation, "T" is the HOT SPOT Temp. in Deg. Kelvin, in the winding, "a" and "b" are constants for the particular Transformer depends upon he Design.
Further RATING FACTOR for the Transformer is also involved, which varies from 1.45 to 2.18 and it is described as follows,
1. Rating Factor 1.45 termed as TRANSFORMER CRITICALLY LOADED.
2. Rating Factor 1.62 to 1.78 termed as TRANSFORMER OVER LOADED.
3. Rating Factor 1.82 termed as TRANSFORMER NORMALLY LOADED.
4. Rating Factor 2.18 termed as TRANSFORMER UNDER-LOADED.
For further details see here
http://www.google.co.in/url?sa=t&rct=j&q=*selection%20criteria%20for%20power%20transformer*&source=web&cd=7&cad=rja&ved=0CFYQFjAG&url=http%3A%2F%2Fstoa.usp.br%2Fjajardini%2Ffiles%2F1724%2F10388%2FCONG1997107.pdf&ei=WE4aUbe0J4fVrQe5-IDIAQ&usg=AFQjCNGLNF4PchFgu-aeAwIJGfBTEJYc8g&bvm=bv.42261806,d.bmk
DHAYANANDHAN.S
02/12/2013 11:28 AM
I for got to add, in my Thread No.11, here is, the Estimated Life for the Transformer for different RATING FACTORS are as follows:
For Sl.No. 1, Estimated life of the Transformer is 3 years
For Sl.No. 2, Estimated life of the Transformer is 15 years
For Sl.No. 3, Estimated life of the Transformer is 30 years
For Sl.No. 4, Estimated life of the Transformer is more than 30 years
DHAYANANDHAN.S
Register to Reply 12 comments
Awf65 (1); Dalton (1); dhayanandhan (2); Joshi (1); lyn (2); nikolay (1); RAMConsult (1); Salar (3)