Conversion from Three Wire to Four Wire

11/20/2012 9:15 AM

I have a cooking range of 2500W which is working on 380V three wire system. (No nuetral) For replacing the same, I am provided with a range of 2500W but four terminals. When connected three terminals , keeping nuetral (terminal no. 4, not sure nuetral or line) floating, heat is reduced. Terminal resistance of old heater shown 110 ohms between 1 & 2 and 1&3, but 220 ohm between 2&3. Terminal resistance of new range shown different values (but high) between all its terminals. I do not know the elements are star or delta connected as they cannot be opened. How a four wire system can be connected into three wire supply without reducing power? If the least/most valued terminal is connected either seriesly or parrellely, can the problem be solved?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: Conversion from three wire to four wire

11/20/2012 9:47 AM

Measure resistance between #1 & all other terminals. Tabulate all the readings.

Measure resistance between #2 & all other terminals. Tabulate all the readings.

Measure resistance between #3 & all other terminals. Tabulate all the readings.

Measure resistance between #4 & all other terminals. Tabulate all the readings.

If it is a 4 terminal 3 phase heater, then you will find one terminal that is common to 3 other live terminals will have identical resistance reading. This terminal then is the common neutral & the rest 3 are the live, phase terminals.

It may even be a 3 terminal device with 4th one being earth, in which case it will have no resistance with other 3 terminals.

Register to Reply Score 1 for Good Answer
Member

Join Date: Nov 2012
Posts: 6
#4
In reply to #1

Re: Conversion from three wire to four wire

11/20/2012 11:30 PM

Hi Mr. Joshi,

Thanks for comment. The resistance betwen terminals are as follows : 1-2=450, 1-3=565, 1-4=225, 2-3=115, 2-4=225 and 3-4=340 ohms. My supply is 380V, 3phase, 3 wired without nuetral. The heater is not provided with a drawing and is sealed. A label in the eqpt shows it is 2500W and 380/400V.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#8
In reply to #4

Re: Conversion from three wire to four wire

11/21/2012 11:27 AM

From your measurements, it looks that:

terminal 1 = L1, 2 = L2 and L3 = 4 will give 2500W at 380V

Configuration looks like: terminal (3)--- 115Ω --- (2) --- 225Ω --- (4) --- 225Ω ---(1)

Since you don't have a Neutral wire, then:

L2 can be connected to either (3), for less heating power, or to (2) for full power.

It all depends on how the different elements are going to be positioned in the oven!!

Register to Reply
Member

Join Date: Nov 2012
Posts: 6
#13
In reply to #8

Re: Conversion from three wire to four wire

12/16/2012 10:31 AM

Your suggestion is absolutely OK. Thanks a lot for the advice. Shorting 1 and 3 solved the problem. Terminals 1, 2 and 4 are connected to L1, L2 and L3 with 1 and 3 shorted.

Regards

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#9
In reply to #4

Re: Conversion from three wire to four wire

11/21/2012 1:52 PM

Your old heater has two identical resistances of 110 ohms in series. #1 is common, between #1 & #2 there is a resistor of 110 ohms, similarly between #1 & #3 there is a resistor of 110 ohms, the load is on 2 phases only. It is connected to three phases, but draws power from two phases only.

Your new heater does not make sense, since ohmic readings are not rational. In this heater, there are three resistors in series. Between #3 & #2 there is a resistor of 115 ohms (please recheck this reading), between #2 & #4 there is a resistor of 225 ohms, between #4 & #1 there is a resistor of 225 ohms. I think this is for 3 phase heater with #3 & #1 joined together for phase 1, #2 for phase 2, #4 for phase 3. You have to run 3 phase 3 wire supply. Neutral is not to be used. I am not comfortable because one of the odd resistor between #3 & #2.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#10
In reply to #9

Re: Conversion from three wire to four wire

11/22/2012 5:06 AM

"It is connected to three phases, but draws power from two phases only."

It will still draw power from the 3 pases.( 110Ω between Ph1 nd Ph2, 110Ω between Ph1 nd Ph3) to make the 2500W~.

On the new Heater: He can bridge terminals 3 and 4 and use that for one of the phases, (Ph3), while 1 to Ph1 and 2 to Ph2. he will get 641 W + 641W + 1255W=2537W.

Now, I don't know how the distribution of the elements is configured within the new range and how the heat will be distributed(?)

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#11
In reply to #10

Re: Conversion from three wire to four wire

11/22/2012 5:37 AM

2.5kW oven seems a bit anemic to me.

What advantage does OP believe he will gain with this undocumented replacement of unstated origin?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#12
In reply to #11

Re: Conversion from three wire to four wire

11/22/2012 10:02 AM

Well, I don't know!

He did not come back to comment!? I hope he is still there.

Register to Reply
Member

Join Date: Nov 2012
Posts: 6
#14
In reply to #11

Re: Conversion from three wire to four wire

12/16/2012 10:42 AM

It is not being used for home, but for a ship. Since the components to be replaced are procured by the company, no choice of merits and demerits. Thank you.

Register to Reply
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Conversion from three wire to four wire

11/20/2012 9:47 AM

Go back to the supplier of the new element and ask for a wiring diagram.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#3

Re: Conversion from Three Wire to Four Wire

11/20/2012 1:17 PM

What is you main supply?: 3 phases without ground, or monofasic (actually two phases plus neutral)?.

What voltage do you read accross the three power lines?

You don't mention a ground wire, have that corrected before someone gets hurt or killed.

Be aware that if you need to re-configure the internal connection of the heaters, well, you can't ! since it is a sealed range according to what you say.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#5

Re: Conversion from Three Wire to Four Wire

11/21/2012 12:51 AM

Just run another conductor of the appropriate size, plus a ground conductor if it's not already there while your at it, and connect the cooking range in the manner that its designers intended.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#6

Re: Conversion from Three Wire to Four Wire

11/21/2012 10:24 AM

"I have a cooking range of 2500W which is working on 380V three wire system".

Why replace If it is working? Anyhow based on your measurements, I believe the old unit is not a 3-phase device! It is powered via a 2-phase 3 wire system, where the 3rd wire as common, with which may also be either connected to a neutral or ground? As dictated by your resistance measurements, terminals 2 and 3 (having 220 ohms between them) are connected across the 380V, while terminal 1, (having 110 ohms with respect to both terminals 2 & 3) being the load center tap and common, can be connected to either earth or neutral.

Using earth as the reference or common to validate the above, you have to measure the power coming out from those 3 wires, but personal Safety always comes first! If you're not sure, get a qualified electrician to do this power supply measurements! Be safe and good luck!!

__________________
vsar
Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#7

Re: Conversion from Three Wire to Four Wire

11/21/2012 11:26 AM

The fourth wire (neutral) should not matter to the heating elements, as they will all be rated for 380V. Based on your resistance values they are connected open delta if you have 3 phase service. If you have single phase service the elements will be in parallel.

The main difference between 3 wire and 4 wire ranges is the controls. Your old range should have a small transformer inside to reduce the 380V to whatever the controls use (probably 220V). The new range does not have an internal transformer and instead relies on a phase to neutral connection to provide the necessary 220V. If you connect 380V to all 4 connections on the new range you will fry the controls.

If your electric service has a neutral wire with the incoming phase conductors, you can run a neutral wire back to your panel and replace the 3 wire receptacle with a 4 wire. If your service does not have an incoming neutral you will need to install a small 380V/220V transformer in the new range to supply the controls.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Joshi (2); LAA_Lucke (3); Muraleedharan Nair (3); pwr2thepeople (1); PWSlack (1); vsar (1); Wal (2); Yahlasit (1)

Previous in Forum: UC3842 and Buck Converter as a Charger   Next in Forum: Controlling High Power LED with DALI or 1-10v

Advertisement