What is the Normal Current Through NGR of 25 MW, 11 KV TG Set

11/21/2012 5:39 AM

Dear all

I observed too much heating in NGR cubical of our TG set. The resistance of our NGR is 62 ohm with 100 A rating. I measured the current through NGR with clamp meter, it is showing 7 amps. As per my calculation, about 3 KW heat energy is being dissipated in NGR box. I think it is sufficient to heat the box. Casing temperature of the box is 94 degree C.

Whether this current is normal in this type of NGR or there is some fault in the system? I have not measured the current through NGR in past, neither I have experienced such heat in our NGR.

I asked the supplier of NGR, they told to measure the 3rd harmonic, it is found 4A. Finally they are saying that it is within the limit. But I am not satisfied with the answer and using cooling fan to cool the NGR from outside.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#1

Re: What is the normal current through NGR of 25 MW, 11 KV TG set

11/21/2012 6:32 AM

It indicates two things:

  1. The protection equipment arrangments around the generator are inadequate, and
  2. There is a phase-to-earth or neutral-to-earth fault in the downstream network, which needs to be eliminated before someone gets hurt/killed by electric shock.

Eliminate the cause. If there is no qualified electrician to hand, hire someone in. Do it now/today/this morning/immediately.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2
In reply to #1

Re: What is the normal current through NGR of 25 MW, 11 KV TG set

11/21/2012 9:34 PM

If not sooner

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#3

Re: What is the Normal Current Through NGR of 25 MW, 11 KV TG Set

11/21/2012 11:05 PM

Sounds a bit excessive.

Turn off the load branch circuits one by one until you find the one that causes the largest change. Start looking for a fault in this branch. If there are no changes noted then get back to us.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#4
In reply to #3

Re: What is the Normal Current Through NGR of 25 MW, 11 KV TG Set

11/22/2012 3:19 AM

It would be rather interesting if the heating effect were unchanged with the generator running completely off load, wouldn't it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#5
In reply to #4

Re: What is the Normal Current Through NGR of 25 MW, 11 KV TG Set

11/22/2012 5:26 AM

Certainly would be.

3kW/24MW= 3,000/25,000,000=0.012%, hmm....I wonder what load the measurements were made at?

Just looking at that resistor "rated" at 100A now. 62ohm makes its rating 62kW, so its working well within its survival range too....

Maybe 3kW is really OK or at least tolerable after all.

The uber hot cabinet could probably do with some better ventilation.

Let's see what OP comes up with.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Commentator

Join Date: May 2011
Posts: 61
Good Answers: 1
#6

Re: What is the Normal Current Through NGR of 25 MW, 11 KV TG Set

11/22/2012 5:34 AM

Calling external agency to analyze the problem. Diagnosis will be communicated to forum.

Register to Reply
Commentator

Join Date: May 2011
Posts: 61
Good Answers: 1
#7

Re: What is the Normal Current Through NGR of 25 MW, 11 KV TG Set

11/22/2012 5:38 AM
DateTimeFrequencyU1 RMSU2 RMSU3 RMSU1 THDU2 THDU3 THDU1 CFU2 CFU3 CFV1 RMSV2 RMSV3 RMSV1 THDV2 THDV3 THDV1 CFV2 CFV3 CFA1 RMSA2 RMSA3 RMSA N-E RMSA1 THDA2 THDA3 THDA1 CFA2 CFA3 CFKF1KF2KF3W1W2W3W TotalWh1Wh2Wh3Wh Totalvar1var2var3var Totalvarh1varh2varh3varh TotalVA1VA2VA3VA TotalVAh1VAh2VAh3VAh TotalPF1PF2PF3PF MeanDPF1DPF2DPF3DPF MeanTan1Tan2Tan3Tan Mean
HzVVV%%%VVV%%%AAAA%%%WWWWWhWhWhWhvarvarvarvarvarhvarhvarhvarhVAVAVAVAVAhVAhVAhVAh
11/20/201212:14:00 PM49.821110011090111000.70.70.71.431.421.426420641064102.62.52.41.461.461.45995.3984.2994.513.11.41.41.31.411.411.42111581291157260795752884172918738073795379902401626468202644768274733180389203676367338161116563871746307392637525719069823887187608855264860.910.910.90.9060.910.910.90.9070.450.460.480.463
11/20/201212:14:05 PM49.811110011100111000.70.70.71.431.431.426420641064102.62.52.51.451.461.45989.3978.3988.413.11.51.51.31.421.411.42111577646456909135716405171837821609615857159304788326350702632859273480580027357336733076142228063491206270456633692618956502176891746917656528140.910.910.90.9060.910.910.90.9070.450.460.480.463
11/20/201212:14:10 PM49.81110011090111000.70.70.71.431.421.426410641064102.72.62.51.461.461.45991.4980.3990.513.11.41.51.41.411.421.42111578147156950915720556171971192412623767238757176826542192651594275407280598861102211013114393347463616296282121634899318992743265252619426474791930.910.910.90.9050.910.910.90.9060.460.460.480.467
11/20/201212:14:15 PM49.81110011090111000.70.70.71.431.421.426410641064102.62.62.61.471.461.46991.7980.7990.913.11.51.51.41.421.411.421115788542570297157285491722006232166316883183195684264429026420542744170803051314695146821525144628636392962852556351916190011003536434924352961055840.910.910.90.9060.910.910.90.9070.460.460.480.464
11/20/201212:14:20 PM49.81110011100111000.70.70.71.431.421.426420641064102.62.62.41.461.461.45990.5979.5989.713.11.41.51.31.421.411.4211157832455697247572301417203506401983960039780119578264075426386802740705802014018363183471905755767635763962786396345425189817034419443644441091319470.910.910.90.9060.910.910.90.9070.460.460.480.464
11/20/201212:14:25 PM49.811110011090111000.80.70.81.431.421.426410641064102.62.62.51.461.461.45990.2979.2989.313.11.41.51.31.421.421.4211157853055699786572511117210202482334751747731143481262820826259632727981798215322013219942284666853635431662756156341834189717655301952360529171582970.910.910.90.9070.910.910.90.9080.450.460.480.462
11/20/201212:14:30 PM49.81110011090111000.80.70.71.431.421.426410641064102.52.62.61.471.461.46993.5982.5992.713.11.41.51.31.421.411.4211158045645719126574471417268405562955546055710167465263654126340592736253800685325675256532664677974637529562965656363088190349476187461106617551847340.910.910.90.9070.910.910.90.9080.450.460.470.462
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8
In reply to #7

Re: What is the Normal Current Through NGR of 25 MW, 11 KV TG Set

11/22/2012 6:42 AM

What were the readings 1 month, 6 months and 1 year ago?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Anonymous Poster #1
#9

Re: What is the Normal Current Through NGR of 25 MW, 11 KV TG Set

04/24/2017 7:38 AM

Hello Dear

I am also facing Same Problem , Please tell the Reason and remedy.

Mobile/Whatsup: +919639006677

Thanks

Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); PWSlack (2); satendrakumart (2); TonyS (1); Wal (3)

Previous in Forum: Invertor Trafo Neutral Grounding   Next in Forum: Earth Leakage Relay

Advertisement