Dear Engineers
how do i select the earth leakage relay( sensitive current rating) of an istallation (eg:250mA,375mA,500mA etc)? any formula/calculation for that.
i have 243kw load, 525Volts, 278A. 150mmsq(supply cable, 100m long), 300A main circuit breaker with shunt trip. so i have to select the size of my earth leakage relay.
please help.
Dan Segami
Good Answers: 34
Re: Earth Leakage Relay
11/21/2012 2:53 PM
Is leakage current, of the order of 250 mA, not dangerous/fatal for personnel? Should you not scale it down to a more rational, safe value?
Good Answers: 181
11/21/2012 9:33 PM
Depends what you want the E/L relay for. Protection against shock or protection of equipment.
11/22/2012 3:17 AM
One could always look up the protocol in good-old British Standard 7671.
11/23/2012 9:12 AM
i want to protect the equipment
Dan Segami
11/23/2012 9:27 AM
in addition, the standard protection for human shock i know is 30mA max. but what i am now asking is for the supply that supplies the heater bank which is used in my plant to dry material. and i will also prefer to use the relay with time delay, but my problem is the size (milli- Ampere rating).
Dan Segami
11/26/2012 8:21 AM
British Standard 7671 is still widely available...