Rooftop Air Conditioner

11/21/2012 8:10 AM

I have a new rooftop airconditioner installed in my deli store. Works OK in the summer but when the outside temperature is 50 - 60 degrees the inside temperature in the store is 78. I asked the technician to fix the problem but he was unable to change the temperature setting when the economizer kicks in. With the cooling equipment in my store, generating a lot of heat, the use of a fresh outside air would be justified at temperature below 50 degrees. Actually it works well on cool days. The technician said that the minimum temperature setting for the economizer is 60 degrees. Is there any way it can be lowered?

Register to Reply
Pathfinder Tags: economizer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#1

Re: Rooftop Air Conditioner

11/21/2012 9:28 AM

Locate the thermostat inside the store, rather that outside.

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#3
In reply to #1

Re: Rooftop Air Conditioner

11/21/2012 9:41 AM

Is not the thermostat, located inside the evaporator in the cooling area, as a normal design/practice?

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#2

Re: Rooftop Air Conditioner

11/21/2012 9:35 AM

Welcome to CR4.

All temp., I suppose are F o

What is the make/type of your Roof-top split AC? Works OK in the summer but at what temp.? Is 50o - 60o F not considered cool? What you need, I think, is adequate air change/ventilation in your store. My train of reasoning could be wrong, due to my living in a different clime.

Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#4

Re: Rooftop Air Conditioner

11/21/2012 10:07 AM

Sounds like you need to escalate the issue to the person who sold you the system, and not let go until you have a satisfactory solution.

What may be happening: 1. This replaces a unit that didn't have an air-side economizer, replaces a smaller AC, or the deli wasn't previously air-conditioned. 2. There is not sufficient exhaust venting for the economizer to make-up enough outside air to maintain the desired inside temperature.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Rooftop Air Conditioner

11/21/2012 11:10 AM

Who on earth needs cooling and dehumidification for personal comfort control at 50-60degF ambient <rhetorical question>? What is needed is simple ventilation. How about switching it off and opening some windows?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#6
In reply to #5

Re: Rooftop Air Conditioner

11/21/2012 12:25 PM

OP's mention of 'economizer' makes me believe that his new unit turns off the compressor and opens an outside-air louver to pull in outside air when ambient reaches 60°F. I suspect he doesn't have enough 'windows' open, i.e. exhaust vents.

Register to Reply
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#10
In reply to #5

Re: Rooftop Air Conditioner

11/21/2012 10:39 PM

Similar to my thoughts. It would surely be more efficient to use fans, not the AC compressor. Would have to take care that drafts are not created that will Offend customers, but if done thru the heating/cooling ductwork that should be OK.

__________________
Lehman57
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Hmmm...

Join Date: Jul 2010
Location: Maryland
Posts: 567
Good Answers: 29
#7

Re: Rooftop Air Conditioner

11/21/2012 12:57 PM

AFIK, residential heat pumps commonly have a thermistor near the compressor/condenser coil. When the ambient temperature drops below about 60oF (~15oC), it won't allow the compressor to run.

It's worth asking the installer if this is the case on your unit.

Register to Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#8

Re: Rooftop Air Conditioner

11/21/2012 6:30 PM

Your situation is similar to trying to paddle with your rudder. In the absence of an oar, this can be a useful adaptation, albiet less efficient and causing more wear and tear than using the proper tool for the job.

What am I trying to convey? When outside air temp is below desired inside air temp, what is needed is adequate air exchange. Using your roof top split AC system to attack the problem is inefficient and causes unnecessary wear and tear, but it works for now. You should upgrade ventilation are soon as practical.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#9

Re: Rooftop Air Conditioner

11/21/2012 7:54 PM

sure it can be lowered. you have to remember that the economizer doesn't wok solely off of outside temp. you always have to take humidity into account. you don't want to add moisture you essentially just paid to remove with your mechanical cooling. so yes it can be lowered if you take the right readings and you understand how to program the economizer correctly, good luck

Register to Reply
Guru

Join Date: Aug 2012
Location: Land of Fruits and Nuts
Posts: 4481
Good Answers: 54
#11

Re: Rooftop Air Conditioner

11/22/2012 12:11 AM

Here is something to consider; if the unit cannot keep the inside of your store cool with an outside temperature of 50 degrees (and inside temp of 78) by simply running the fan only, then there is something wrong with your system. My guess is that the fan isn't blowing enough air (too low CFM) or the vent system has too much resistance.

A fairly inexpensive solution would be to put a large fan on the ceiling (something like a whole house fan). Get a belt drive unit and install it where your customers will not complain about the wind and noise. Maybe in the back room? The whole house fan will pull plenty of air from the inside of the store and exhaust it out the roof. Be careful of negative pressure in the store (you may need to keep a door open). You'll be surprised how quickly the store will cool. IF you don't want to keep the door open, try windows or run the a/c system on fan only.

This solution will be the least expensive, because trying to troubleshoot a rooftop a/c system isn't going to be cheap.

Good luck and let us know what you do.

__________________
Enjoy and be happy! Life is too short!
Register to Reply
Participant

Join Date: Nov 2012
Posts: 2
#13
In reply to #11

Re: Rooftop Air Conditioner

11/25/2012 5:00 AM

Thanks. I really got a lot of help from the Forum Thread. Now I know that I have to install a vent or two for the heat to be vented out. My deli store is divided by the front store and kitchen in the back where there is even more heat generated by ovens and two walk-in coolers. The space above drop ceiling is open in the whole area, so the heat from the kitchen goes to the front store above the ceiling. My plan is to install two vents, one above the walk-in coolers in the back and another in the front to remove the hot air gathered above the drop ceiling. I believe that the biggest problem comes from a poor design of the heating & cooling system which wasn't modified when the space was converted from an office to a deli store years ago.

Register to Reply
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#14
In reply to #13

Re: Rooftop Air Conditioner

11/25/2012 8:23 PM

I'm not a ventilation engineer, so squawk if I'm wrong. If possible put the new vents on the downwind side. In order for hot to vent out, makeup air has to come in someplace--does that place exist? It might be preexisting leaks. Remember that this make-up air will be outside temperature, and will have to be conditioned.

__________________
Lehman57
Register to Reply
Commentator

Join Date: Oct 2010
Posts: 55
Good Answers: 2
#12

Re: Rooftop Air Conditioner

11/22/2012 9:52 AM

To much talk and no action! Get the unit name plate data, include the economizer also. The problem is not hard just lower the economizer switchover point to a temperature that matches the discharge air temperature when the A/C is running. The equipment may not have come setup to do this, but without the data no good solution can be found.

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#15

Re: Rooftop Air Conditioner

11/28/2012 6:39 PM

HAVE A CONTROLLER WITH A WIDER RANGE INSTALLED IN ORDER TO HAVE THE ECONOMIZER SUPPLY 55 DEGREE AIR. iF YOUR SPACE IS COOLED TO 78 WITH 60 DEGREE AIR, 55 DEGREE AIR SHOULD GIVE YOU A SPACE TEMPERTURE FIVE DEGREES COOLER...73, A VERY CONMFORTABLE TEMPERATURE. ACTUALY, 78 ISN'T ALL THAT BAD IF YOU ARE IN A DRY CLIMATE, SUCH AS DENVER, COLORADO.

LOU BINDNER

Register to Reply
Guru

Join Date: Jun 2010
Posts: 989
Good Answers: 14
#16

Re: Rooftop Air Conditioner

12/17/2012 10:36 PM

fresh air make-up vent is too small and your building is too tight.

You need a way to relieve the pressure buildup inside the building when outside air is below 60 degrees and your unit is pulling in fresh air instead of re-circulating cooled air. Someone didn't have their Duct-U-Lator with them the day they installed the fresh air make-up vent.

http://compare.ebay.com/like/290762941371?var=lv&ltyp=AllFixedPriceItemTypes&var=sbar

Register to Reply
Guru

Join Date: Jun 2010
Posts: 989
Good Answers: 14
#17
In reply to #16

Re: Rooftop Air Conditioner

12/17/2012 10:38 PM

Also, you don't say if you have a cooktop hood running all the time. If so it is pulling all the new cool air right back out before it can circulate in the room.

Register to Reply
Register to Reply 17 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

129CBRider (2); Autobroker (1); bigg (2); Doorman (1); Fredski (1); Joshi (2); Lehman57 (2); Lo_Volt (1); Lou Bindner (1); philroth2252 (1); PWSlack (1); truth is not a compromise (1); Ziggy2 (1)

Previous in Forum: Useful Websites for Self-Builds & Projects   Next in Forum: Windmill Failure

Advertisement