Incoming Fluctuating Power Supply

11/22/2012 1:57 PM

Dear Friends, I have a 12kv power supply incoming to the plant, This supply is then step down through a 2.5MW transformer with an auto tapchanger to 480vac to my switchgear. However the tapchanger is left in manual. I am now experiencing fluctuating in the voltage. what can I do to recitfy this? and what kind of failure can I expect on my equipment?

__________________
electrotech
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: Incoming fluctuating power supply

11/22/2012 2:14 PM

Is the voltage fluctuation present on all the three phases? What is the level of change in voltage?

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Incoming fluctuating power supply

11/22/2012 2:53 PM

There is SO much you haven't told us!!!!!!!!!!!!!!!!!

Where are you?

Have you talked to your power supplier?

WHAT HAVE YOU DONE?

Maybe hiring a local electrician would be the best thing to do.

This is the best free advice you will get all day!!!

Register to Reply
Anonymous Poster #1
#3

Re: Incoming fluctuating power supply

11/22/2012 3:15 PM

Change your name until you know what to ask and/or do.

Register to Reply Score 1 for Off Topic
Member

Join Date: Nov 2012
Location: Trinidad and Tobago WI
Posts: 5
#10
In reply to #3

Re: Incoming fluctuating power supply

11/23/2012 4:52 PM

Hi I know what to do, may be you could come out in the open and identify your self.

__________________
electrotech
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: Incoming Fluctuating Power Supply

11/22/2012 10:38 PM

Why did you leave an auto-tap changer in manual position?.

__________________
pnaban
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #4

Re: Incoming Fluctuating Power Supply

11/23/2012 3:14 AM

Good question.

Sadly, there isn't a Good Question button, only a Good Answer one.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Oct 2010
Location: Hyd - IND
Posts: 21
#5

Re: Incoming Fluctuating Power Supply

11/22/2012 11:53 PM

See Mr.Electrotech, if the output voltage of the transformer is low than the rated we can increase by changing the tap position but here u have mentioned its fluctuating, u have to tell what is the fluctuation level and normally fluctuations may occur incoming side only due to variable transsmission & distribution losses, commonly it may exists for few minutes. please find out incoming side also(12kv) fluctuation is there or only in outgoing of the transformer (480v). if its 12kv side u have contact ur power supply provider, but if exits in 480V side we have to cross check the transformer load side in ideal position (ie with out load), in ideal position of the transformer fluctuation is not there means u have to check ur loads due to over load also fluctuations will occur.

__________________
Shaju Khan
Register to Reply
Member

Join Date: Nov 2012
Location: Trinidad and Tobago WI
Posts: 5
#8
In reply to #5

Re: Incoming Fluctuating Power Supply

11/23/2012 6:38 AM

Thank for your answer, I know what i have to do because it is coming from the incoming I know that I have to put the Auto tapchanger on auto so it could compensate when the voltage fluctuate.

__________________
electrotech
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #8

Re: Incoming Fluctuating Power Supply

11/23/2012 7:10 AM

What revolutionary thinking...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#11
In reply to #8

Re: Incoming Fluctuating Power Supply

11/23/2012 11:55 PM

Has there been a reduction in the fluctuations since you have allowed the tap changer to do its job?

I really can't understand why you had it running in manual, they are not an inexpensive piece of equipment and are fitted for a reason.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Incoming Fluctuating Power Supply

11/23/2012 3:15 AM

The size of the fluctuations is of interest. Were it inside +/- 10% on the LV side, don't worry about it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856