Clarification with Generator Neutral Earthing, Neutral Link and Neutral Out

11/24/2012 9:23 AM

The generator neutral out is earthed for attaining two targets. (1) for a getting zero potential in neutral and hence balanced voltage (2) for benefiting a return path, so that overload or earth leakage could be sensed and to protect.

The neutral link is provided because to isolate the earthing in case of testing or so.

CT for EFR is kept after NL

CT for REF is kept before NL

If the arrangement (2) is correct, I believe EFR-CT could sense the earth (leakage) current and REF-CT could sense the residual current in between neutral & earth. But, by the arrangement (2) if any loose contact with NL, voltage unbalancing may occur. So, many prefer (1), if REF is not there.

Please discuss.

__________________
Assistant Electrical Inspector, Govt. of Kerala, India
Register to Reply
Pathfinder Tags: generator neutral earthing
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Clarification with generator neutral earthing, neutral link and neutral out.

11/24/2012 9:36 AM

You seem so conflicted.

The NVR is not balanced, therefore the BFD will not be in phase with the EFR nor the ABC/MCb.

The return path is not clear here, so the RTB period will be longer.

Reversing the NL with the CT will help the NFR, but the only sure cure is two aspirin and a NAP.

OT.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#2

Re: Clarification with Generator Neutral Earthing, Neutral Link and Neutral Out

11/24/2012 12:00 PM

CT for REF is kept before NL: What your REF stands for?

CT for EFR is kept after NL: Your EFR, does it stand for earth fault relay or emergency frequency relay?

And what is your NL stand for?

Neutral Link? Why do you need it & for what kind of testing?

Can we see a sketch of your system incorporating all these?

By the way are your seniors, members if this forum? If not, please invite them to this August forum.

Register to Reply
Associate

Join Date: Dec 2007
Location: Kochi, Kerala, India
Posts: 27
#3
In reply to #2

Re: Clarification with Generator Neutral Earthing, Neutral Link and Neutral Out

11/24/2012 1:15 PM

REF - Restricted Earth Fault Relay

EFR - Earth Fault Relay

NL -Neutral Link

Testing Means - Insulation Reading Measurement - In such occasions, the earth connection may need to be disconnected.

__________________
Assistant Electrical Inspector, Govt. of Kerala, India
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#4

Re: Clarification with Generator Neutral Earthing, Neutral Link and Neutral Out

11/24/2012 2:32 PM

Neutral isn't about getting balanced voltages, Guv. Neutral is about providing a route for the imbalance current on single-phase loads. At least, it was when I went to classes.

__________________
Good moaning!
Register to Reply
Associate

Join Date: Dec 2007
Location: Kochi, Kerala, India
Posts: 27
#5
In reply to #4

Re: Clarification with Generator Neutral Earthing, Neutral Link and Neutral Out

11/24/2012 10:47 PM

If the neutral is not strongly earthed, the phase voltage which is getting in between phase and neutral will be unbalanced. This is what I meant.

Anyway, please refer to my route doubt. Which connection is advisable (1) or (2) in the diagram? If my query is not clear, I am ready to give again clarifications.

__________________
Assistant Electrical Inspector, Govt. of Kerala, India
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6

Re: Clarification with Generator Neutral Earthing, Neutral Link and Neutral Out

11/25/2012 2:23 AM

To put your question precisely, you want to know whether neutral distribution should be before the REf CT or after the REf CT. Is it so?

Register to Reply
Associate

Join Date: Dec 2007
Location: Kochi, Kerala, India
Posts: 27
#7
In reply to #6

Re: Clarification with Generator Neutral Earthing, Neutral Link and Neutral Out

11/25/2012 4:28 AM

Yes, there lies a point.

For REF protection to locate internal faults, we use 3 line CTs and one neutral CT. I have shown only the neutral CT with the diagram. It should sense the neutral current, which is the total of the three line currents. In a balanced condition, this neutral current must be zero. When some internal fault occur, an unbalancing will occur and the net current will cause the REF relay to trip. The neutral earthing path gives a return path for any earth faults/leakages, which causes a current ('Ie') to travel. Let actual neutral current be, In (without 'Ie'). So, total neutral current (to the generator side) will be 'It' = 'In' + 'Ie'. The REF sensing CT in the neutral path should read 'It' and not 'In'. Am I right? If so, the CT should be located to read 'It'. With connection (1) in the diagram the REF CT can not read 'It', instead only 'Ie' will be sensed. So, connection (2) is preferable. Please analyse.

__________________
Assistant Electrical Inspector, Govt. of Kerala, India
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8
In reply to #7

Re: Clarification with Generator Neutral Earthing, Neutral Link and Neutral Out

11/25/2012 9:35 AM

I am a trainer with L & T and conducting protective relay training programme is my cup of tea. I have thoroughly analysed the prepositions and have made a presentation on the same. But, being a computer novice, I am unable to post them here directly. However, if you can send me your mail ID thro this forum's mailbox, I will be able to send you the presentation by mail.

Register to Reply
Associate

Join Date: Dec 2007
Location: Kochi, Kerala, India
Posts: 27
#9
In reply to #8

Re: Clarification with Generator Neutral Earthing, Neutral Link and Neutral Out

12/03/2012 9:13 AM

After an alround search, I conclude here below the clarification which I asked. Neutral out need to be from the incoming side of NL, before which REF CT is to be included. All other details remain same, as I explained earlier.The final diagram shall be as follows.I welcome, any more doubt if there.

__________________
Assistant Electrical Inspector, Govt. of Kerala, India
Register to Reply
Member

Join Date: Oct 2011
Location: Qatar
Posts: 8
#10
In reply to #8

Re: Clarification with Generator Neutral Earthing, Neutral Link and Neutral Out

09/09/2013 5:15 AM

Dear EE65,

I know I am visitng this thread after long time, however , I am faced with similiar situation now. In case you can share your above mentioned presentation, it would be great help to me as well.my mail id is mailtodkp at gmail do com.

Best regards

dinesh