Previous in Forum: What is Diversity Factor?   Next in Forum: How to Estimate Cable Tray Weight Onboard?
Close
Close
Close
3 comments
Rate Comments: Nested
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2

Can We Use Class-X CT in Place of 5P10?

11/28/2012 11:47 PM

hai all,

Is there any techincal prblm if we are using cl-x ct in place of class 5P10, because i need IDMT/inst. overcurrent protection only, but the ct available in the switchgear is cl-x only it is an existing panel the cl-x ct was already there in the panel kept as spare. there is no space for add one more set of ct's. it is a 415V 2275kVA generator.

thanking you,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Jan 2011
Posts: 12
Good Answers: 1
#1

Re: can we use class-x ct in place of 5P10

11/29/2012 7:12 AM

More detailed spec of the Cl-x ct are required..like turns ratio,Voltage knee point,Maximum magnetizing current at Voltage Knee point, Maximum resistance of the secondary winding. Here ALF also not known.

Risks of unwanted tripping or no-operation under fault conditions...

Regards,

Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#2
In reply to #1

Re: can we use class-x ct in place of 5P10

12/02/2012 6:28 AM

sir, the ct ratio - 4000/1A, vk=800V, Rct-16ohms, i think the difference between cl-x and 5p10 are mainly in saturation point ie vk. so this might be suitable for the requirement.

thanks

Register to Reply
Active Contributor

Join Date: Dec 2011
Posts: 13
#3
In reply to #1

Re: can we use class-x ct in place of 5P10

12/21/2012 1:22 AM

He supplied your data!

Register to Reply