Boiler Drum Level

12/02/2012 8:49 AM

Aftr the annual shutdown of our 135MW BOILER when we started our boiler we encountered this problem of boiler drum level control fluctuating. The DCS transmitters reading r varying we checkd it n found ok. If we take 0mm as drum datum level then gauge glass reading is varying as -40 mm level and electrode level hydrastep is showing around +50mm. The drum level control in Auto mode is fluctuating alot evn though MS press is constant at full load. we tuk drum control in manual mode yet it is fluctuating at full load causing lots of problems. Before annual shutdown we never faced this problem

__________________
"No matter how hard the past,you can always begin again."
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jan 2011
Posts: 668
Good Answers: 3
#1

Re: Boiler Drum Level

12/02/2012 7:21 PM

could it have an air lock?

Register to Reply
Associate

Join Date: Sep 2012
Posts: 33
Good Answers: 1
#2
In reply to #1

Re: Boiler Drum Level

12/02/2012 8:25 PM

As far as i consider we have given proper venting n drum vent was closed only aftr free flow of water was ensured coming out frm vent...at around 5kg/cm2

__________________
"No matter how hard the past,you can always begin again."
Register to Reply
Associate

Join Date: Jan 2011
Location: Rotorua, New Zealand
Posts: 30
Good Answers: 1
#3

Re: Boiler Drum Level

12/03/2012 12:01 AM

First, did you fill up the reference leg before start up? Second, if you did not, and if you are using a 2oo3 voting, then give each transmitter a good blowdown. It will take about an hour for the signal to settle down. Surprised you said you had water coming out the vent. On start up the vent valve at the top of the drum is left open until about 2 Bar pressure then it is closed, but that has nothing to do with this problem. If the level signal is fluctuating then Auto mode makes the control worse. Is the feed water pressure constant downstream of the control valve? How many transmitters do you have and where are they mounted?

__________________
Allan Evans
Register to Reply Score 1 for Good Answer
Associate

Join Date: Sep 2012
Posts: 33
Good Answers: 1
#4
In reply to #3

Re: Boiler Drum Level

12/03/2012 1:55 AM

Drum vent was open during boiler hydro test...to ensure proper venting. Total there r three transmitters n arrangement is like one set consists of one frm steam side at top of drum n one fr water side bottom side of drum. we have flushed the transmitters yet its not helpd much.

__________________
"No matter how hard the past,you can always begin again."
Register to Reply
Associate

Join Date: Jan 2011
Location: Rotorua, New Zealand
Posts: 30
Good Answers: 1
#5
In reply to #4

Re: Boiler Drum Level

12/03/2012 2:58 AM

Are all three transmitters fluctuating?

__________________
Allan Evans
Register to Reply
Associate

Join Date: Sep 2012
Posts: 33
Good Answers: 1
#6
In reply to #5

Re: Boiler Drum Level

12/03/2012 8:16 AM

All the three transmitters r fluctuating. We have done flushing twice yet its reading are +22mm; -11mm; -48mm. The average value is taken as median for reference and its fluctuating coz of all three values varying.

__________________
"No matter how hard the past,you can always begin again."
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: Boiler Drum Level

12/03/2012 9:32 AM

The boiler might be priming. How close to the blowdown current set point is the current total dissolved solids level?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Aug 2012
Posts: 35
Good Answers: 2
#8

Re: Boiler Drum Level

12/03/2012 10:46 AM

Do agree with the previous post. If you had just overhauled the boiler there must be a lot of grease and oil in the boiler drum water. Normally one does a boiling out and an additional input of anti- foaming and Alkalinity booster chemicals. Your pH within the boiler drum should be gradually built up to 10.0 - 11.5. I suppose this has been done.

The other interesting issue is the discussion of blowing down/flushing the transmitters. You should be having a HP and LP impulse piping from your Steam Drum coming down to connect with the Drum level transmitter. At the top of this impulse piping you should have a refill plug. Once you have flushed this piping, you should refill the entire impulse piping with water and then close the plugs. Has this been done or is the impulse piping empty?

You could have fluctuating levels due to both these reasons .

Register to Reply
Associate

Join Date: Sep 2012
Posts: 33
Good Answers: 1
#9
In reply to #8

Re: Boiler Drum Level

12/03/2012 12:55 PM

Well during shutdown we had replaced the entire eco tubes coils with new ones. Though acid or alkaline cleaning must hv been done but due to some reasons it did not happen. Aftr v did hydro test i gues the iron particles got settld in drum though v did 3 times flushing entire water frm eco. The iron content is high means conductivity is highr than permissble levels whn we were doing light up but due to load schedule tie up we went ahead finally synchronisng machine with grid aftr gvg an entire blowdown..again via emptyng hotwell n gvg make up at same time. regarding hp ip impulse line i wud find out as i am not sure about it.

__________________
"No matter how hard the past,you can always begin again."
Register to Reply
Power-User

Join Date: Mar 2007
Location: Kansas
Posts: 159
Good Answers: 9
#10

Re: Boiler Drum Level

12/05/2012 12:07 AM

Is the water quality too high? We have seen times when we needed to add ammonia to the feedwater in order to get a reading. I wouldn't think that this would be the problem as you just recently brought the unit back up. The water should have high silica for a while. There is still the possibility that the conductivity of the water (it is demineralized) is too low to get a stable reading. Perhaps your ammonia injection system is not pumping very well. (Just a suggestion.)

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!