What are the advantages & disadvantages of using Vacuum contactor with fuse instead of Vacuum Circuit breaker in the HT system?
Re: Advantage of Vacuum contactor
12/07/2012 5:11 AM
Oh, at a guess, the need for more components and an electrician to change the fuse when it blows, whereas the circuit breaker might be reset by an operative. Economics?
Re: Advantage of Vacuum Contactor
12/07/2012 8:42 AM
It is 10-20% cheaper. Motor with frequent start-stop shall use vacuum contactor instead of circuit breaker. Vacuum contactor is designed for millions on/off operation while CB isn't.
Good Answers: 181
12/07/2012 4:41 PM
That's a sweeping statement.
12/09/2012 3:34 PM
Whoa there, that isn't true for high voltage vacuum contactors and switchgear at all. Tens of thousands yes, but not millions.
France - Member - New Member
12/10/2012 7:57 AM
Electrical endurance :
a contactor is rated at a minimum of 300 000 operations (Schneider SF6 rollarc contactor) and easily up to 1 million for vacuum contactors, whereas circuit breakers have a rated endurance of 10 000 operations.
Downstream cable protection :
In case of fault at the motor terminals, for instance, a fused contactor will limit the I²t , when a circuit breaker will have much slower protection . A fused contactor will allow you to size the conductors at the cross section needed by the motor amperage, withous having to take care of their short circuit withstand .
06/13/2016 8:45 AM
Vacuum contactor is planned for millions on and off operations. Contactors are useful in commercial and industrial applications.