Anonymous Poster #1

Repeated Cable Failures in 34.5 kV Cables

12/11/2012 8:00 AM

We are facing repeated cable failures in a 4000 m long MV Cable circuit with following details;

  • Cable: 1x300 mm2/25mm2 Cu/TR-XLPE/HDPE
  • Cable is approximately 30 years old.
  • Laying is in tre-foil formation in duct bank.

A brief history of the tripping due to faults is as under;

  • 1st Tripping: Earth fault located, repaired and circuit energized on 9th day.
  • 2nd Tripping: After 11 days of energization, fault occured on other cable. The fault was located, repaied and circuit energized after 10 days of the incident.
  • 3rd Tripping: The circuit tripped again, just after 24 hour of energization! This time again, on different cable and different section.

What could be the possible cause(s)/reason(s)/factor(s) behind such failures?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Repeated Cable Failures in 34.5 kV Cables

12/11/2012 8:07 AM

What - apart from the digger bucket breaking it or the earthquake fracturing it?

Er, um, it's a bit tricky.......oh.....it's overloaded? No, the overcurrent protection would have operated first.......hmmmmm.........oh.....got it! It's too old!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Good Answer (Score 2)
3
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Repeated Cable Failures in 34.5 kV Cables

12/11/2012 8:12 AM

As stated↑

Cable is approximately 30 years old.

Replace it now.

You've already lost over 20 days of down time. When will down time cost more than cable replacement?

I'd get on with fixing the problem and quit patching the old cable.

REPLACE THE CABLE.

Reply Good Answer (Score 3)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: Repeated Cable Failures in 34.5 kV Cables

12/11/2012 12:02 PM

If the cable is 4000 m long then has to be 6-7 junction boxes on each cable.

Junction box is located -usually -in a manhole. If the manhole was flooded the water could penetrate the cable in the junction box vicinity.

If the duct is not "embedded duct" but is laid directly underground and the pipe is PVC made [and the cable is not armored] then could be termite attack.

__________________
Julius
Reply
Associate

Join Date: Sep 2012
Posts: 33
Good Answers: 1
#4

Re: Repeated Cable Failures in 34.5 kV Cables

12/11/2012 12:31 PM

If the failure is occuring in a particular place within the same junction box change it immediately...its seems like moisture has entered there. Changing entire cable length is not possible but in this case being 30 yrs old i would suggest you to change it part by part......

__________________
"No matter how hard the past,you can always begin again."
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5

Re: Repeated Cable Failures in 34.5 kV Cables

12/11/2012 1:57 PM

From the information given (and unless something has happened recently to damage or degrade the cable insulation) the cables appear to be at or over their end of life (in your particular application) and are starting to fail.

Have you performed a detailed analysis of the failed sections of the cables to find out what the failure could be due to?

I would talk directly with the cable manufacturer (or someone similar if they have gone out of business) and get their advice on the expected cable life.

__________________
jack of all trades
Reply
Power-User

Join Date: Sep 2007
Location: Sheboygan, WI USA
Posts: 372
Good Answers: 13
#6

Re: Repeated Cable Failures in 34.5 kV Cables

12/11/2012 10:43 PM

Some years ago I read of long cables needing surge protection, on the cable side of the breaker, as the cables are a big capacitor, if the breaker opens and recloses there could be 1.76x line volts or there abouts applied due to phase change.

I didn't see a diagram showing if you have a generator or motor on the end of this cable ? The gen/motor should have surge protection at its terminals.

__________________
"I believe we are masters of our lives - we hold all the cards and it is up to us to use them right." Vesna Vulova - survived 33,000ft fall
Reply
Commentator

Join Date: Dec 2011
Posts: 67
#7

Re: Repeated Cable Failures in 34.5 kV Cables

12/12/2012 12:34 AM

What type of repairing u have done so far...?

it seem s the issue is still there & u are ignoring it

Reply
Commentator

Join Date: Dec 2012
Posts: 65
Good Answers: 3
#8

Re: Repeated Cable Failures in 34.5 kV Cables

12/12/2012 2:53 AM

The cable is old. But, the failure modes you describe don't suggest failure from insulation breakdown. It sounds like you are getting "hot spots" in your cable assembly. You should check for high levels of harmonics in the feed source and in the load. You might also have a faulty ground bond at a transformer at either end of the run. Check your transformers, if they are running at temperatures over their rated operating levels for the loads they carry you probably have a harmonic problem. If your environment includes allot of VFD's or high frequency power supplies then you can almost be certain that is your problem. That combined with the age of the cable adds up to "hot spy" failures in your cable!

Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#9

Re: Repeated Cable Failures in 34.5 kV Cables

12/12/2012 3:38 AM

"You might also have a faulty ground bond at a transformer at either end of the run".

I think DogOfWar could be right. Usually Medium Voltage System it is an ungrounded system or High Resistance Grounded System. In this case one phase accidentally grounded raises the potential between Ground and two other phases to 34.5 kV [instead of 34.5/sqrt(3)] and if the cable shield is grounded the insulation is strong stressed.

__________________
Julius
Reply Score 1 for Good Answer
Member

Join Date: Feb 2012
Location: Trinidad & Tobago
Posts: 7
Good Answers: 1
#10

Re: Repeated Cable Failures in 34.5 kV Cables

12/12/2012 6:06 AM

Hey brother, it is time to replace the cable. It is said that XLPE cables have suffered from "treeing". This is encouraged by testing such as Hipot. Also as said by another contributer, if you have VFD's then dont even think further...proceed to replace. I always do an RCA to know "what" happened and this is recommended as a learing exercise that we share with the less learned members of the Maintenance or Operations team.

Reply
Reply to Forum Thread 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (2); CoronaCameraMan (1); DogOfWar (1); iftikhar129 (1); jack of all trades (1); lyn (1); PWSlack (1); Trini (1); vir540 (1)

Previous in Forum: CO2 Fire Fighting Discharged During Lightning Storms   Next in Forum: Calculate the Radius of Cable Tray

Advertisement