Anonymous Poster #1

Ex d Protection

12/19/2012 8:36 PM

Can Ex d equipment be installed in Zone 2? I believe it can only be installed in Zone 1. If so can some one please provide a reference to a clause in an IEC standard?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Ex d Protection

12/19/2012 8:54 PM

Ex d equipment designed for Zone 1 can indeed be installed in Zone 2 which is a safer environment than Zone 1. Yes it is commonly not marked to indicate such which can lead to confusion.

As for where it is in the standard, it is a little vague but try Annex G of IEC 60079-1 Equipment protection by flameproof enclosures 'd'.

Think of it like an IP rating, IP66 offers a better liquid ingress protection than IP65 so an IP66 box can be used in an application calling for an IP65 box.

Alternatively you can contact the equipment supplier for more information or written documentation if the customer requests it (although the site inspector should know all this).

__________________
jack of all trades
Reply Good Answer (Score 3)
Anonymous Poster #1
#2
In reply to #1

Re: Ex d Protection

12/19/2012 9:06 PM

Thanks.

Reply
Commentator

Join Date: Dec 2011
Posts: 67
#3

Re: Ex d Protection

12/20/2012 3:01 AM

any equipment designed for zone 0 & 1 can be utilized in zone 2 as well but dn't forget the cost impact..............

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Ex d Protection

12/20/2012 3:22 AM

What <...cost impact...>? If it is suitable for zone 1 then it is suitable for zone 2 with zero additional cost.

What is the cost of not using it? Explosions? Loss of life? <rhetorical questions - NNTR>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Aug 2010
Location: Wales, UK
Posts: 391
Good Answers: 18
#5
In reply to #4

Re: Ex d Protection

12/20/2012 4:00 AM

Hi,

I think he means you don't need to buy a Rolls Royce to do the shopping when a Mini will do.

Have a Merry Christmas and a Happy New Year,

John

__________________
Best advice I can give as you get older "Never miss an opportunity to relieve yourself"
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Ex d Protection

12/20/2012 4:01 AM

IEC 60079 gives all.

Please stop and attend a suitable training course before carrying out any further hazardous area electrical design, construction, alteration or testing work.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Commentator

Join Date: Dec 2011
Posts: 67
#7

Re: Ex d Protection

12/20/2012 4:30 AM

yeah as we move from zone2 to zone0, the cost of equipment increases & vice versa..

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #7

Re: Ex d Protection

12/20/2012 8:42 AM

Some equipment suitable for zone 2 cannot be installed in zone 1 and some equipment suitable for zone 1 cannot be installed in zone 0, then there are installations suitable for zone 0 that can be created in zones 1 and 2 as well.

The assertion of increased cost with reducing zone number label is nonsense.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Commentator

Join Date: Dec 2011
Posts: 67
#9

Re: Ex d Protection

12/20/2012 10:47 PM

PWSlack are u really confirmed it is nonsense?

Think for a while if zone 2 equipment can't be used in zone1 or zone 0 & zone 0 equipment can be used in zone 1 & zone 2 then what is the factor of consideration.

surely it is the increased protection for zone 0 & lesser for zone2.

for more protection you will have to bear more cost........

Reply
Reply to Forum Thread 9 comments