Wind Span and Weight Span Etc. Calculation

12/23/2012 4:18 AM
Tower Type

(a)

Basic Span Ruling Span Wind Span Weight Span Max. Individual Span

2)

S1/D1 340 360 1.2 a 2.0 a 1.4 a
SA/DSA 340 360 1.2 a 2.0 a 1.4 a
TA/DTA 360 360 1.2 a 2.0 a 1.4 a
TA45/

DTA45

360 360 1.2 a 2.0 a 1.4 a
TA90/

DTA90

340

(0.5 a)1)

360 1.2 a 3.0 a 1.2 a
ST/DST 1500 0.95 a 1.2 a 3.0 a 1.2 a
STT 700 0.95 a 1.2 a 3.0 a 1.2 a
TT/DTT/

TTT

300

(0.5 a)1)

360 1.2 a 3.0 a 1.2 a

Is this the standard? How are wind span and weight span values are derived?

Regards,

sks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Mechanical Engineering - New Member Fans of Old Computers - TRS-80 - New Member Popular Science - Weaponology - New Member Safety - Hazmat - New Member Hobbies - Fishing - Fish On! United States - Member - New Member

Join Date: Apr 2012
Location: Detroit MI, USA
Posts: 2496
Good Answers: 271
#1

Re: Wind Span and Weight span etc. calculation....!!!

12/23/2012 4:48 AM

When looking at the transmission line profile view, the wind span is defined as half of the sum of adjacent spans. The weight span is defined as the distance from low point sag of one span to the low point sag of the next span.

To clarify, these values have to do with loading of a supporting structure (transmission line pole structure). with 3 structures in a row, there are 2 cable spans. One half of the sum of the 2 spans will give the wind span. This will be used to calculate the force applied to the structure due to a horizontal wind blowing on the conductors.

Because the cable takes the form of a catenary curve when hung between 2 fixed points, there will be a low point between each of the structures. The distance between these low points will be the weight span for the middle structure. This value will be used to calculate the weight of the cable that the structure must support.

__________________
How we deal with death is at least as important as how we deal with life. --CAPTAIN KIRK, Star Trek II: The Wrath of Khan