Explosion for the Lightning Arrestor

12/26/2012 3:21 PM

Dear all

I got today's explosion for the lightning arrestor which was install in 132kv transmission line for s/phase .tاhe Explosion happened when the circuit breaker for this line its closed.the qusition is What are the possible reasons for explosion the lightning arrestor

thanks for all

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: explosion for the lightning arrestor

12/26/2012 3:47 PM

Without any data about line configuration, voltage rating, operating conditions, what might have changed, how it failed, etc., etc., it is impossible to give more than the obvious answers; i.e., transient switching overvoltage, improperly sized arrestor, severely contaminated arrestor.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Explosion for the Lightning Arrestor

12/26/2012 7:42 PM

The obvious reason is that the circuit breaker closed. Duh.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Explosion for the Lightning Arrestor

12/26/2012 10:08 PM

The lightning arrestor died instead of the more expensive equipment. I do not see a problem here.

Now if lightning did not take out this lightning arrester and none of your engineers are willing to explain how their design was either miswired, used faulty components or a fault in the design itself was the root cause then you will have to hire a licensed engineer to investigate.

Save and document all failed components for your in house or independent investigator.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4

Re: Explosion for the Lightning Arrestor

12/26/2012 11:40 PM

Sounds to me like that arrestor "took one for the team" ie it did its job.

More information please.

Also clarify that when you say the CB is "closed" it is in the ON position (the terms open and close as relating to switches can transpose with language, eg opening the light switch means turning on the light here)

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Commentator

Join Date: Oct 2011
Posts: 95
#5

Re: Explosion for the Lightning Arrestor

12/27/2012 3:47 AM

May due to defective unit of lightning arrestor . Whether you performed testing on lightning arrestor before installation .

Whether there is a chance for corona discharge ?

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6
In reply to #5

Re: Explosion for the Lightning Arrestor

12/27/2012 4:04 AM

Lightning arrestors go bang sometimes. When they do it's a good thing. Unless it was installed too close to other equipment without segregation and collateral damage has occurred. An arrestor is a darn sight less costly then what they normally protect.

How do you propose testing the arrestor without destroying it or accelerating the onset of a smoke release episode once in service?

Corona discharge.....normally associated with high energy events. Normal. Clutching at straws on that one.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#7

Re: Explosion for the Lightning Arrestor

12/27/2012 9:44 AM

The most likely reason is the breaker closed in on an already failed arrester. Arresters typically fail in a short circuit. Although you didn't mention the reason the breaker was open, it may have opened to clear the failed arrester.

Register to Reply
Commentator

Join Date: Sep 2012
Posts: 58
#8

Re: Explosion for the Lightning Arrestor

12/27/2012 3:15 PM

Dear all

thanks for all

Can anyone tell me why voltages increase when the breaker is closed and what level rise if the breaker in the 132kv network

Regardes

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#9
In reply to #8

Re: Explosion for the Lightning Arrestor

12/27/2012 4:05 PM

Your engineer should be able to tell you why closing a breaker will change the voltage. Your engineer should know what is connected on either side of that breaker. We do not know this, so we cannot help you.

Just don't open the other breaker that I'm pointing toward. I'm not done yet. You'll have to answer to my wife if you do.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#10
In reply to #8

Re: Explosion for the Lightning Arrestor

12/27/2012 5:40 PM

I'll venture a guess and say that plasma had something to do with the explosion, if you want to get down to brass tacks.

You want to know why voltage increases when you close the input to a circuit? Are you serious? Is there another way you can configure your question in order to ensure you get an accurate answer?

__________________
common knowledge...less common than common sense
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: Explosion for the Lightning Arrestor

01/02/2013 7:37 AM

One of the possibilities is that there was a mongoose crawling past the lightning arrester when the breaker was closed.

Or it might have been a snake. It's a bit difficult to see the charred remains of whatever-it-was from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply