Heat Recovery in Steam Generator

01/01/2013 8:01 AM

can i recover heat from flue gas after passing from esp of a boiler which is having a temperature of 131deg for heating dm water having 70deg by a heat exchanger?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: heat recovery in steam generator

01/01/2013 8:25 AM

Yes, you can.

You will want to determine if the cost of installation of such a system can be justified by the savings in energy used to heat the water.

Register to Reply
4
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#2

Re: Heat Recovery in Steam Generator

01/01/2013 10:53 AM

Dear srik231,

The Answer is YES. We can Recover Heat from flue gas after ESP.

But several factors to be considered before we install the Heat Recovery Equipment. The Factors are

1. DEW POINT of the Combustion Product.

2. Level of Heat Recovery desired.

3. Permissible Pressure Loss in the Heat Recovery System.

4. If condensation takes place - how to avoid.?

5. Type of fuel used, and its fineness, its abrasion nature on the Heat Recovery Area.

6. Finally Whether It is ECONOMICAL.?

DHAYANANDHAN.S

Register to Reply Good Answer (Score 4)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#3

Re: Heat Recovery in Steam Generator

01/01/2013 11:41 AM

thats co-generation......been around for decades......so yes, you can

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Heat Recovery in Steam Generator

01/02/2013 8:25 AM

That sounds like the way a domestic condensing central heating boiler works, so yes, it can be done. The materials of construction of the proposed heat recovery unit need to be resistant to attack from sulpuric acid, which will be formed when condensing the exhaust from a sulphur-containing fuel, and to attack from nitric acid, which is formed in small quantities in the condensate from most fuels; recovering the energy in the flue gas brings these materials below their dew point, as other readers above have pointed out, and they will be expelled from the system as liquids. Clearly the local drainage system will need to be resistant to attack also, and the facility's effluent discharge consent limits will need to be assessed for the prospect of an effluent with lower pH.

Apart from those considerations, go for it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Mar 2007
Location: Kansas
Posts: 159
Good Answers: 9
#5

Re: Heat Recovery in Steam Generator

01/02/2013 5:36 PM

Another thing to consider is how much induced draft is required to get the flue gas out of the boiler and up the stack. Some systems require reheating the flue gas to get better lift or natural draft to actually get the flue gas up the stack. At one time (and laws change occasionally) flue gas was required to get at a certain altitude in order to carry away from the boiler. Newer local environmental rules may have reduced that requirement so you should at least consider the laws regarding your particular boiler before making any modifications. Any engineering studies can also defray errors and cost overruns if these laws are taken into consideration before getting into the project very far. If there is a requirement for certain height of stack emissions, removing heat from the flue gas may cause efficiency gains in one area to be negated by additional costs in another area. Say for instance... heavier loading of induced fans.

Register to Reply
Register to Reply 5 comments