Anonymous Poster #1

Megger Value

01/02/2013 7:52 AM

Happy New Year Everyone,

After megger test in 415V LV Switchgear Bus Bar, Reading comes at 300 Megaohm for Y-B & B-R Phase, however it is only 70 MegaOhm for R-Y Phase. I checked all the bolts tightness and surface of Bussbar for any external materials and spacing, it is all ok. can you suggest me what will be the problem and how to rectify it to get nearby reading in all three phases.

Thanks.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Megger Value

01/02/2013 9:07 AM

Remove the spider's web hanging between the R and the Y busbars.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Anonymous Poster #1
#8
In reply to #1

Re: Megger Value

01/05/2013 7:31 AM

It is new installation hence no spider web sorry...

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Megger Value

01/02/2013 9:13 AM

"can you suggest me what will be the problem": Imbalance in the system

"and how to rectify it to get nearby reading in all three phases." Call an electrician out to fix it.

Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: Megger Value

01/02/2013 11:02 AM

70 megohms on 415V electrical insulation is acceptable. There are always some variations in resistance between phases - you will NEVER get them exactly the same. All it takes is a little dust on one of the insulators, a little moisture in an area that gets less ventilation, or something minor like that to give you the difference.

What is your insulation resistance to ground? That is also important.

__________________
To get the right answers, first you need to ask the right questions.
Reply Score 1 for Good Answer
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#4
In reply to #3

Re: Megger Value

01/02/2013 4:08 PM

we'll never know but....if he warms the general area and takes his readings again they'll probably change...due to moisture

Reply
Anonymous Poster #1
#9
In reply to #4

Re: Megger Value

01/05/2013 7:33 AM

I Used Space Heater for a day....Reading did change marginally(now 82 mega ohm) but no where near 300 or so.....Damn!

Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#5

Re: Megger Value

01/03/2013 4:41 AM

With everything disconnected you would expect almost infinity. I go with the looking for things like spiders and similar debris.

Checking things for tightness will not increase the insulation value.

While it is in bits I suggest a ductor test. Now on this test clean and tight joints really will make the difference. If might be this test will unearth something. You are looking for a really low value.

A flash test might clear the spiders but its a little harsh .....

Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#6

Re: Megger Value

01/03/2013 1:08 PM

Is it Delta or Wye wiring?

Reply
Anonymous Poster #1
#7
In reply to #6

Re: Megger Value

01/05/2013 7:27 AM

it is Wye

Reply
Associate

Join Date: Feb 2011
Location: Angul, orissa
Posts: 25
Good Answers: 1
#10

Re: Megger Value

02/20/2013 11:44 AM

I hope there is a control transformer for that bus bar system. If it is so, the primary of that transformer must have been fed from R and Y phases. It might be because of the insulation level of that particular MPCB which is feeding that trafo that the megger value between R and Y phase is comparitively low.

__________________
mscs
Reply
Reply to Forum Thread 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); Fredski (1); lyn (1); MSCS (1); Munster (1); PeterT (1); PWSlack (1); silverfox (1)

Previous in Forum: Soldering Piezoelectric Igniter   Next in Forum: Why Autotransformers Always Starts at Zero Position ?

Advertisement