Single Phase To Ground Fault In Star-Star Transformer

01/16/2013 1:00 AM

If single pahse to ground fault occures in HV side of a star-star transformer where neutral of the both sides are grounded, what reflection will come to LV side? HV side is connected to the generator and load is connected to the LV side.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: single phase to ground fault in star-star transformer

01/16/2013 3:13 AM

If there is a phase-to-ground fault then a protection device will operate, disconnecting the fault.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Nov 2012
Posts: 142
Good Answers: 14
#2

Re: Single Phase To Ground Fault In Star-Star Transformer

01/17/2013 12:24 AM

You are likely to experience over excitation and saturation of the metal core and possible overheating of the transformer due to increased currents in the unshorted phases. This can cause the windings to burn out or even a fire if the transformer is oil immersed. Although you are probably already seeing 3rd harmonics, you may also experience more induced harmonics in the secondary due to the unbalanced primary. These will cause a distortion of the secondary waveform.

You don't say if the primary star is connected to the generator star or simply earthed at the transformer, results can vary with these differences.

Register to Reply
Participant

Join Date: Jan 2013
Posts: 2
#3
In reply to #2

Re: Single Phase To Ground Fault In Star-Star Transformer

01/17/2013 1:50 AM

The primary and secondary stars are simply earthed. The primary star is not connected to the generator star .

I want to know whether the zero sequence current will also flow in secondary windings or only there will be distortion of the secondary waveform caused by third harmonics.

Register to Reply
Power-User

Join Date: Nov 2012
Posts: 142
Good Answers: 14
#4
In reply to #3

Re: Single Phase To Ground Fault In Star-Star Transformer

01/17/2013 4:12 AM
Register to Reply
Participant

Join Date: Nov 2012
Posts: 2
#5
In reply to #3

Re: Single Phase To Ground Fault In Star-Star Transformer

01/18/2013 12:19 AM

definetly there s a provision for the flow of zero sequence component of currents in the system since the fault is associated ground.. these zero sequence currents may not flow if ur windings are connnected in delta.

Register to Reply