Anonymous Poster #1

Cable Lug

01/18/2013 8:28 AM

Dear All

What is the disadvantage/advantage if i using cable lug 1 size below of the cable. because some cable lug do not have the same size of the cable.

Regard

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#1

Re: Cable Lug

01/18/2013 9:55 AM

The terminal [lug] is a power cable most of failure location.

The terminal has to withstand the maximum permitted steady state and short-circuit current of the cable. Then you must use a suitable tool to crimp it and a suitable length and strength. See the following:

http://www.klauke.com/fileadmin/pdf/Produkte/BRDESONDERDR108GB_DE_Sonderdruck_GB.pdf

First of all as the conductor could be solid, stranded [usually class II (B), compressed or compact, round or sectorial the lug has to fit all the possibility in one lug. So you may use a metric conductor in an AWG destined lug but very close [as 300 MCM lug for 150 mm^2 conductor.]

__________________
Julius
Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#2

Re: Cable Lug

01/18/2013 10:47 AM

An advantage is, it may be a field expedient solution: use what I have on hand, get this installation finished so I can go home.

A disadvantage may be the subsequent unscheduled undesirable thermal event.

__________________
Semper Ubi Sub Ubi
Reply Score 1 for Good Answer
Active Contributor

Join Date: Jan 2013
Location: Abu dhabi, UAE.
Posts: 21
#3

Re: Cable Lug

01/18/2013 11:33 AM

Actually,

Usage of under size lug is not an issue...! Mostly we found that little lower size of lug will not have much thermal co-efficient of differenance. So, use then same what you have...!

Also, as far as you are sure about load end. B'coz after fixing the lug immediately you

will not leave it as it is. No need to get confuse. Go ahead with fixing the job. Then, you can arrange all the required and specific material.

All the best....!

__________________
sudhir_g_thombare
Reply Score 1 for Off Topic
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Cable Lug

01/18/2013 1:46 PM

If you are referring to a mechanical lug, they usually have a range of wire size they will accept. If you use wire smaller than the lowest in the approved range, there is a risk that it will pull out of the lug under fault conditions and cause an arc flash event that could hurt or kill someone and / or start a fire.

If you are referring to a compression lug, it is illegal in most places with reasonable safety laws to use a compression lug on any wire that it is not SPECIFICALLY listed to be used on. So using a lug that is one size smaller than the wire is not only likely impossible without trimming strands off of the wire and thereby changing the current capacity of it. This will expose the perpetrator as being the party responsible for the ensuing fire, arc flash, death and disfigurement of whomever is around it when it fails.

Other than that, no problem.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
Anonymous Poster #1
#5
In reply to #4

Re: Cable Lug

01/19/2013 4:25 AM

Hi All

Due to no available of 1.3mm cable lug, i've use 1.5mm cable lug prior to testing.

Regard

Mohd

Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#6
In reply to #4

Re: Cable Lug

01/19/2013 3:10 PM

Friends,

JRaef has given you a very pithy but correct answer. The reason it is "illegal in most places" is because the electrical codes (NEC and probably others) specify that components must be installed in accordance with their listing directions. In other words, if the product has installation (or maintenance) instructions or limits by the testing agency's listing, you must comply with these or be breaking the law.

Some crimping tools will take a wide range of lugs and crimp them onto a smaller wire with no problems because of their design. They will usually include instructions that show this work to be acceptable even if the components used do not give the permission. That is because you have 4 components in play--the wire, the lug, the tool, and the installer.

Be smart--ensure that your work will meet codes, so you minimize future liability.

--JMM

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Cable Lug

01/20/2013 3:16 PM

One disadvantage might be dismissal from post, following some undesirable catastrophic self-disassembly event at the lug, perhaps?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8

Re: Cable Lug

01/20/2013 10:14 PM
__________________
The reports of my death are greatly exaggerated.
Reply
Reply to Forum Thread 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); Anonymous Poster (1); Doorman (1); jmueller (1); JRaef (1); PWSlack (1); sudhir_g_thombare (1); TonyS (1)