Transformers Connections

01/20/2013 12:31 AM

I have one 3ph 75 kVA Delta Wye dry type transformer 480 V pri -120/208 sec. Can I reconnect this transformer to be used as 50kVA a single ph 480-120/240V? The third transformer in the core will be disconnected and shunted.

Register to Reply
Pathfinder Tags: Transformer connections
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#1

Re: Transformers connections

01/20/2013 1:50 AM

' Can I reconnect this transformer to be used as 50kVA a single ph 480-120/240V?'

No

'The third transformer in the core will be disconnected and shunted.'

How exactly it look like 'disconnected and shunted'

__________________
When was last time you did something for first time.
Register to Reply
Participant

Join Date: Jan 2013
Posts: 3
#7
In reply to #1

Re: Transformers connections

01/22/2013 9:45 AM

Disconnected and shunted means that the third transformer of the bank in the common core will not be tied to the input and output lines. Shunted means the installation of one jumper on the secondary and primary coil leads to prevent it to work as a CT. I understand that if I leave them opened it can blow up if there is any current flowing thru. Am I correct?

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#2

Re: Transformers connections

01/20/2013 10:46 AM

Yes you can. Just make sure you use the outer two winding assys and that they are wire identically in phase with each other.

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#3

Re: Transformers Connections

01/20/2013 1:37 PM

Transformer can be connected for single phase.

Connection for single phase is the same as for 3 phase, except one phase is left unconnect. Primary and secondary of unconnected phase can be either open circuit or shorted.

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4

Re: Transformers Connections

01/21/2013 7:51 AM

First of all, you are not going to get 50kVA out of it - instead you will get smoke if you try to load it with 50kVA load on one phase for too long. Each of the 3 windings of the transformer will be nominally rated for 25kVA (adds up to 75kVA for the 3 together), so connecting to 2 phases of the primary and the associated phase of the secondary phase-to-neutral picks up ONE winding, and will give you 25kVA of 120V single-phase. And you cannot get 240V out of this arrangement no matter how you connect it. Draw the phasor diagram and you will see. Watch out for those disconnected phases! They will have a voltage on them, but not what you want.

Much better to buy the right transformer for your application.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5
In reply to #4

Re: Transformers Connections

01/21/2013 12:01 PM

Yup... you got it. Have a GA point on me.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#6

Re: Transformers Connections

01/21/2013 2:13 PM

You can get 120/240V 50 kVa from this transformer.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Jan 2013
Posts: 3
#8
In reply to #6

Re: Transformers Connections

01/22/2013 10:20 AM

This is what I want to do. But have a doubt of what will happens with the third transformer that is in the same core but disconnected. Naming the leads of the secondary on the two transformers to be in service; A & B for xmer no 1 and C & D for the second transformer; I think A & D are the live leads and B&C connected together is going to be the neutral point. Between A & C, I should obtain 240 volts and 120 to neutral. The primary connection is: both transformers connected in parallel as the drawing you have posted. I just want to be sure this connection is correct and no damage will occur to the transformer.

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#10
In reply to #6

Re: Transformers Connections

01/22/2013 2:08 PM

Carl Pugh, I see you're correct. I should have drawn the winding diagram, not the phasors.

I originally thought that if it could be done, one would need to chop up the winding connections within the transformer. However, I think it can be done at the manufacturer's supplied terminals. For the primary, if you label the terminals A, B, C from top to bottom, you can simply jumper C to A, and connect the 480V across A/C and B. This effectively shorts together the third winding so it is not used. You could probably then get away with just taping off the C-phase secondary terminal (that winding shouldn't develop any voltage) and use A, B, and N as the output connections.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#9

Re: Transformers Connections

01/22/2013 12:47 PM

The connection shown will absolutely positively work. However to be on the safe side it is probable advisable to:

Contact the transformer manufacture and obtain his advice.

Use a variable transformer and raise the input voltage slowly while monitoring the input current.

If a variable transformer is not available, use a resistor to limit the input current and quickly disconnect the input voltage is the current is too high.

4 large 120V incandescent light bulbs in series make a low cost resistor for this use.

The unused coil can have the primary shorted or open. Or grounded or floating.
The same for the unused coil secondary.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: Transformers Connections

11/25/2022 9:27 AM

How did the phone calls with the transformer manufacturer go?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 11 comments

"Almost" Good Answers: