Transformer Oil Testing, BDV.

01/23/2013 12:40 PM

Hey all !

Am working on 132KV/11KV transformer. Recently we performed a BDV test. The mean value for 6 tests was 77KV.

Now my question is that when a transformer winding has 132KV going through it then how is that 77KV BDV value is acceptable ... Shouldn't be more than 132KV ???

I know the NEC, IEC rules but want to know the logic behind accepting the values.

Thanks !

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Transformer Oil Testing, BDV.

01/23/2013 1:36 PM

If what you say is accurate, and the transformer is energized, then you are operating on borrowed time! It's time to de-energize the transformer and find out why the BDV (Break Down Voltage) is so low, probably by doing a DGA (Dissolved Gas Analysis). The DGA will point you in the proper direction for cleaning/replacing the oil, and/or an internal inspection. You need someone experienced in these matters on-site ASAP.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Participant

Join Date: May 2011
Posts: 4
#4
In reply to #1

Re: Transformer Oil Testing, BDV.

01/24/2013 1:18 AM

@RAMConsult.

The BDV value is not low. Its quite healthy infact by international standards ! But I would like to know the logic as to how this BDV value is considered ok. I just posted the following ...

"But let me elaborate my confusion; by International standards the oil is considered good for insulation in 132KV/11KV transformer if BDV value is greater than 55KV.

Now how will the oil be a good insulation medium for 132KV when the oil itself has a BDV value of 75KV ???

Does it has something to do with the way BDV testing is done ??? I mean electrode spacing is 2.5 mm when conducting BDV testing.... in real condition the winding spacing inside the transformer is much larger so 75KV would be good enough ???

Plz explain !"

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #4

Re: Transformer Oil Testing, BDV.

01/24/2013 3:14 AM

See #1↑.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Apr 2012
Posts: 1
#13
In reply to #4

Re: Transformer Oil Testing, BDV.

01/28/2013 3:05 PM

According to iec standard BDV is the break down voltage per 2.5 mm spacing between Live conductors, this 2.5 mm is not the actual spacing between electrodes of dielectric test set, infact it's a standar set to measure the break down strength of transformer oil for a minimum spacing of 2.5 mm. while In oil transformer spacing between live conductors are much larger than 2.5mm, so 77 kv BDV is acceptable for 132 and even 220kV transformer.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Transformer Oil Testing, BDV.

01/23/2013 3:08 PM
Register to Reply
Participant

Join Date: May 2011
Posts: 4
#3
In reply to #2

Re: Transformer Oil Testing, BDV.

01/24/2013 1:05 AM

Thanks for your replies. But let me elaborate my confusion; by International standards the oil is considered good for insulation in 132KV/11KV transformer if BDV value is greater than 55KV.

Now how will the oil be a good insulation medium for 132KV when the oil itself has a BDV value of 75KV ???

Does it has something to do with the way BDV testing is done ??? I mean electrode spacing is 2.5 mm when conducting BDV testing.... in real condition the winding spacing inside the transformer is much larger so 75KV would be good enough ???

Plz explain !

Register to Reply
3
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#5
In reply to #3

Re: Transformer Oil Testing, BDV.

01/24/2013 2:22 AM

First, you need to learn a lot about electrical transformer and insulation.

Second, it's as follows:

The 75 kV value corresponds to 2.5 mm as you said.

The voltage in 132 kV winding you get between the ends of a winding. If the winding is eg. 1000 mm long the actual insulation level is

75 kV x 1000/2.5 mm = 30000 kV

When considering the insulation within the winding Think at the fact that between consecutive loops the voltage is 132 kV / no of loops per winding (roughly) , and it may be of about a couple of kV ( a lot less than your 75 kV even at 2.5 mm spacing). Moreover, the windings have also paper insulation.

Hope it helps

__________________
The time is ......now
Register to Reply Good Answer (Score 3)
Participant

Join Date: May 2011
Posts: 4
#6
In reply to #5

Re: Transformer Oil Testing, BDV.

01/24/2013 2:30 AM

Hey Nikolay !
Thanks for your answer, it really helped. I was thinking on the same track but just needed someone to confirm it. Been a great help, thanks again :) !

Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#9
In reply to #6

Re: Transformer Oil Testing, BDV.

01/24/2013 8:18 AM

Glad to help.

Remember though that what I wrote is just the over simplified answer to your question. The real things are a bit more complicated than this.

Tchuss

__________________
The time is ......now
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#8
In reply to #3

Re: Transformer Oil Testing, BDV.

01/24/2013 5:33 AM

In 1970s we tested BDV with a gap between electrodes of 4mm at 40 kV(10kV/mm) for 33kV transformer. Have the test standard changed?.

__________________
pnaban
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#10
In reply to #8

Re: Transformer Oil Testing, BDV.

01/24/2013 8:48 AM

There are two common test procedures for oil dielectric used here in the US (and many parts fo the world) per ASTM: The D-877 which uses flat-faced cylindrical electrodes spaced at 2.5mm, and the D-1816 which uses spherically-shaped electrodes spaced at either 1mm or 2mm. There are other slight differences between the two tests (rate of voltage increase, agitation of sample, etc.), but with regard to the electrodes this is the difference.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#11
In reply to #10

Re: Transformer Oil Testing, BDV.

01/24/2013 9:11 AM

We were following the BS with spherical electrodes.

__________________
pnaban
Register to Reply
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#12

Re: Transformer Oil Testing, BDV.

01/24/2013 10:51 AM

What should be Break Down Voltage value for the following Transformers?

1. 22/0.4kV, 1000kVA

2. 0.4/125 KV, 160.9 KVA

3. 132/6.3 KV, 26 MVA

Above three transformers having different voltages. Take Higher side Voltages

1. 22,000 V

2. 125, 000 V

3. 132, 000 V

According to IS 6792:1992

The oil sample is subjected to steadily increasing alternating voltage until breakdown occurs in a BDV test kit. The Breakdown voltage is the voltage reached at the time of spark appears between the electrodes. The test is carried out six time on the same cell filling and the Electric strength of the oil is the arithmetic mean of the six result obtained. The Electrodes are mounted on the horizontal axis with the test spacing of 2.5 mm. The values should be

30 KV Minimum: Transformers up to 72.5 KV

40 KV Minimum: Transformers from 72.5 KV up to 170 KV

50 KV Minimum: Transformers from 172 KV up to 420 KV

Example-1: 22/0.4kV, 1000kVA

The BDV value should be greater than 30 KV (Voltage is 22000 V)

Example-2: 0.4/125 KV, 160.9 KVA

The BDV value should be greater than 40 KV (Voltage is 125,000 V, greater than 72,500 V)

Example-3: 132/6.3 KV, 26 MVA

The BDV value should be greater than 40 KV (Voltage is 132,000 V, greater than 72,500 V)

Hope it would help

Register to Reply Score 1 for Good Answer
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Adeel (3); Aghvel Niazi (1); m4_mehdee (1); nikolay (2); PeterT (1); pnaban (2); PWSlack (1); RAMConsult (1); wareagle (1)

Previous in Forum: IEC Standards   Next in Forum: Connection of Logic Meter

Advertisement