Connection of Logic Meter

01/24/2013 1:35 AM

Dear Friends,

We need to connect a logic meter to an existing LV Switchboard and MCC with star delta starters for 3 pump motors.

Please advise at what location we should connect the CT and the link for the voltage.

Kind regards and thank you

Register to Reply
Pathfinder Tags: Logic Meter
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Connection of Logic Meter

01/24/2013 4:00 AM
  • Voltage?
  • Maximum power?
  • Supply cable size?
  • How much space is available in the MCC?

Etc.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Mar 2012
Posts: 48
#2
In reply to #1

Re: Connection of Logic Meter

01/24/2013 4:46 AM

Dear Sir,

Thank you for your response.

The voltage is 400V and each motor is rated at 132 kW, 2 duty; 1 standby. There is not adequate space in the MCC and we need to install the meter on the wall besides the panel. My question is: at what point shall we install the CT and connect the voltage link.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Connection of Logic Meter

01/24/2013 4:57 AM

The CT needs to go around one of the three phase conductors, as shown in the installation manual supplied with it. One might reasonably expect three such devices, not one. CTs are current devices, and the need for a <...voltage link...> is currently abstruse.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply