What are the conditions/factors of using a HV cable for LV application?
Re: HV cables
01/28/2013 4:39 AM
The sanity of the designer would be one of them.
Re: HV cables
01/28/2013 5:59 AM
The purpose of cables is to transfer power from one place to another. At LV, a cable is capable of transferring far less power than at HV, as the cross-sectional-area [CSA] of the conductor is far smaller than a suitable cable for the same power at LV. Further, there is a deficit of cable management equipment and techniques for using HV cables for LV applications. So it is far better to use the correct equipment for the job.
One wouldn't use a 50cc moped to travel from London to Vladivostock; why would one use an HV cable for an LV application (rhetorical question - NNTR)?
Re: HV cables
01/28/2013 1:45 PM
Now now, some people may want to wire their house up in 50mm2 33kV XLPE screened cable.
Re: HV cables
01/28/2013 5:00 AM
why would you do that? cables cost money, you know?
“For no man can forbid the spark nor tell whence it may come.” ? Francis Bacon
Re: HV cables
01/28/2013 5:02 AM
The most common condition/factor:functional insipience exceeds minimum detectable levels.
Re: HV Cables
01/28/2013 1:43 PM
Sheer desperation.
Re: HV Cables
01/28/2013 6:26 PM
Cost plus Gubmint job?
Re: HV Cables
01/29/2013 5:58 AM
HV cable is already in stock and is surplus!!!
Gajanan Phadte
Good Answers: 42
Re: HV Cables
01/29/2013 9:31 AM
If you already have this cable- as gmphadte said- and you cannot sell it and buy a cheaper low voltage instead of, then you may use it but there are some restrictions:
If a screen or shield exists you have to ground it and just in a single point.
Second, as insulation is thicker a derating factor will be necessary-in open free air
mainly. The shield also-even grounded at one end-will add some watt/feet to overall losses. But the derating factor is still not important.
The permissible bending radius will be less- due to shield presence. The shield copper could facilitate steel corrosion on contact-if any.
Julius
Good Answers: 42
Re: HV Cables
01/30/2013 5:51 AM
My mistake: "The permissible bending radius will be less- due to shield presence" has to be:
"The permissible bending radius shall be bigger- due to shield presence".
Julius
Re: HV Cables
02/07/2013 12:43 AM
Hi , try using MV cable for the intermediate sections