Circuit Breaker Design

01/29/2013 3:55 AM

Why the electrical designer choosing MCCB for the above 63A rating feeder instead of MCB and choosing ACB for the above 800A rating feeder instead of MCCB?

Register to Reply
Pathfinder Tags: circuit breaker
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Circuit breaker design

01/29/2013 3:56 AM

At a guess, perhaps the wiring downstream of the MCCB is only sized for a 63A load? Without seeing the installation it is difficult to say much more.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Circuit breaker design

01/29/2013 4:19 AM

...except that MCCBs probably are unavailable for 800A breaking current capacity.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#3

Re: Circuit Breaker Design

01/29/2013 7:00 AM

MCBs (Miniature Circuit Breakers) and usually only available up to 63A, so above that, MCCBs (Moulded Case Circuit Breakers) or ACBs (Air Circuit Breakers) are used. MCCBs take less space, but ACBs are more cost-effective above about 630A.

So it's a trade-off of cost, space and availability.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4

Re: Circuit Breaker Design

01/29/2013 8:09 AM

In addition to what others have said, MCB/MCCB/ACB usage is also guided by the need to discriminate upstream and downstream breakers. The subject is vast, and you can get some good knowedge from the web. One example here: Merlin Gerin CB discrimination