Why the electrical designer choosing MCCB for the above 63A rating feeder instead of MCB and choosing ACB for the above 800A rating feeder instead of MCCB?
Pathfinder Tags: circuit breaker
Re: Circuit breaker design
01/29/2013 3:56 AM
At a guess, perhaps the wiring downstream of the MCCB is only sized for a 63A load? Without seeing the installation it is difficult to say much more.
01/29/2013 4:19 AM
...except that MCCBs probably are unavailable for 800A breaking current capacity.
Re: Circuit Breaker Design
01/29/2013 7:00 AM
MCBs (Miniature Circuit Breakers) and usually only available up to 63A, so above that, MCCBs (Moulded Case Circuit Breakers) or ACBs (Air Circuit Breakers) are used. MCCBs take less space, but ACBs are more cost-effective above about 630A.
So it's a trade-off of cost, space and availability.
India - Member - New Member
Good Answers: 164
01/29/2013 8:09 AM
In addition to what others have said, MCB/MCCB/ACB usage is also guided by the need to discriminate upstream and downstream breakers. The subject is vast, and you can get some good knowedge from the web. One example here: Merlin Gerin CB discrimination