Two Main Switchgear

01/29/2013 2:50 AM

Hi,

We will mount a 4 MVA 34,5/0,4 KV medium voltage transformer.

We have to use 2 main switchgear at LV side .

One switchgear will feed one machine the other one will feed second machine.

Do we have to use a machanical or electrical between two switchgear?

Kind Regards,

Musa UÇAN

__________________
Unbalance Fault
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Two main switchgear

01/29/2013 3:50 AM

The answer to the question may be determined by stating whether the machines may run concurrently or whether they must not. Once this has been decided, the rest is detailed design.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Dec 2012
Posts: 1
#2

Re: Two Main Switchgear

01/30/2013 2:17 AM

Do you mean providing mechanical and electrical interlock facitlity for the two incoming swithgears? If you want to have an alternate power source in case one of the transformers is down and there is essential or critical loads require power supply. Just provide a coupler VCB between the two incoming switchgears. You may need to do load sharing as one transformer may not be able to take care all the electrical loads.

Register to Reply
Associate

Join Date: Jun 2011
Location: ROUEN (in NORMANDY), 120 km from Paris, France, Europe, Earth, Sun Sytem, Milky Way, Universe.
Posts: 39
Good Answers: 3
#3

Re: Two Main Switchgear

01/30/2013 2:16 PM

Hello folks,

No devices are useful. Your LV swgr has to make the protection and the discrimination between your two engines. If you don't have any MCR, put an electrical contact (in X) in each trip coil of your outgoings, in order to cut both outgoing in case of a transformer fault. One motor can run with the other tripped. The transformer protection will not see any trouble. It is a standard case of running. After that, all depends of your case of motor runnings. But this is the minimum you have to do. If you have no MCR, it is more complicate. It is a litanie of tripping contacts, that i can not describe here. Be careful to start each engine with a slight delay between them. If not the starting voltage could be seen as a fault by the transformer protection.

Good year and good luck

BRZK

__________________
That's all, Folks. Take some time to learn where you live...
Register to Reply
Participant

Join Date: Oct 2012
Posts: 2
#4
In reply to #3

Re: Two Main Switchgear

01/30/2013 3:59 PM

Very good answer sir; we did same at a Coca Cola facility, to solve a problem. Delay was not long enough and we had to calibrate for that.