Anonymous Poster #1

Heater Elements

01/30/2013 4:23 PM

Can you use a motor overload to protect heating elements?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#1

Re: heater elements

01/30/2013 4:32 PM

Do you know how an overload protects a motor ?

Do you know how a heating element works ?

It doesn't seem so.

__________________
An obstacle is something you see when you take your eyes off the goal.
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: heater elements

01/30/2013 4:33 PM

Protect it from what? A motor overload does just that... protect a motor from an overload. How do you overload a heater element?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: heater elements

01/30/2013 4:59 PM

I'd think it could act as its own overload.

Reply
Anonymous Poster #1
#4

Re: heater elements

01/30/2013 5:09 PM

I guess the answer is NO

Reply
Guru
Engineering Fields - Mechanical Engineering - New Member Fans of Old Computers - TRS-80 - New Member Popular Science - Weaponology - New Member Safety - Hazmat - New Member Hobbies - Fishing - Fish On! United States - Member - New Member

Join Date: Apr 2012
Location: Detroit MI, USA
Posts: 2496
Good Answers: 271
#5

Re: heater elements

01/30/2013 5:18 PM

Yes, if you powered it from Russel's pinwheel device.

__________________
How we deal with death is at least as important as how we deal with life. --CAPTAIN KIRK, Star Trek II: The Wrath of Khan
Reply
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: heater elements

01/30/2013 5:54 PM

To expand on what has been said:

Electrical circuits must be protected from the damage that can happen to the insulation in the even of a short circuit and a long time increase in current and the heat associated with the conductors carrying it. So at a basic level, the protection just has to keep the distribution conductor insulation from failing. That is what a fuse or circuit breaker is for. But inside of a motor, the winding insulation is different from the feed conductor insulation and is in some ways more susceptible to damage. A motor thermal overload is designed based on the thermal "damage curve" of the motor windings (and rotor). This is a somewhat unique issue in the electrical protection world, so it took a special device for that. If the Thermal Overload Rely protects the motor, it by default will protect the conductors feeding the motor.

If you have a resistive heater element, the "damage curve" of the heater element is higher than the feeder conductors going to it. So there is no need for the added protection a Thermal Overload Relay provides. But a TOL does NOTHING to provide protection against a short circuit, so a fuse or CB is required in the circuit anyway. Since the fuse or CB will be protecting the wire, the TOL is redundant and therefor unnecessary.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 4)
Commentator

Join Date: Dec 2012
Posts: 65
Good Answers: 3
#10
In reply to #6

Re: heater elements

01/31/2013 2:41 AM

Au contrare' mon ami! No TOL will lead to disaster..... If the thermal output of the heating element is constrained, thermal runaway will occur. As the temperature rises, element resistance will increase, and lower current will flow, as the temperature continues to rise.....if lucky, the element melts, shorts out to ground, and blows fuse/CB. If unlucky....FIRE! The current needed to melt the element will be well below the fuse/CB rating needed to protect the supply wiring!

Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#13
In reply to #10

Re: heater elements

01/31/2013 8:42 AM

Au contraire au carre...

How is the overload relay expected to detect the problem if the overheated heater's resistance increase and the current decreases? The overload relay will not react.

The only protection here is a temperature sensor or an element resistance sensor. As for the protections when the element fails, fuses are usually the best to limit the collateral damages.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply
Commentator

Join Date: Dec 2012
Posts: 65
Good Answers: 3
#14
In reply to #13

Re: heater elements

01/31/2013 11:49 AM

Pretty much precisely what I stated. The TOL here is a simple thermal fuse, or more often a Klixon thermal breaker that self resets. Standard stuff in HVAC electric heating design, clothes dryers, hair dryers, Mr Coffee, etc etc etc!

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7

Re: Heater Elements

01/30/2013 6:31 PM

In addition the motor overload generally controls a contactor coil to disconnect the motor load rather than breaking the full motor load so you would also need a contactor (unless possibly the heater is really low current).

Just another reason why the answer is no.

__________________
jack of all trades
Reply
Guru
Engineering Fields - Optical Engineering - Member Engineering Fields - Engineering Physics - Member Engineering Fields - Systems Engineering - Member

Join Date: Apr 2010
Location: Trantor
Posts: 5363
Good Answers: 647
#8

Re: Heater Elements

01/30/2013 8:00 PM

In my case it often happens that the motor burns up to protect the fuse. It usually works with expensive electronics equipment, too.

__________________
Whiskey, women -- and astrophysics. Because sometimes a problem can't be solved with just whiskey and women.
Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#9
In reply to #8

Re: Heater Elements

01/30/2013 11:51 PM

Generally the main components of the motor starter i.e SCPD (fuse or MCCB), contactor and thermal overload relay are properly selected to comply with the requirements of Type 2 co-ordination as per IEC. The curve of the thermal overload relay should be below the hot withstand curve of the motor. if the commponents are properly cordinated then the TOL will de-energise the contactor before the motor burns due to overload.

In case of short circuit the fuse/ MCCB will protect the motor as well as the contactor by disconnecting the power circuit. Contactors are not suitable for breaking higher current (typically 10 times of the rated current). Thus the fuse/ MCCB rating is so selected that in case of short circuit the SCPD will operated much faster than the TOL.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: Heater Elements

01/31/2013 3:29 AM

Not according to British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#12

Re: Heater Elements

01/31/2013 7:27 AM

You could IF YOU KNOW how to select it and HOW to wire it!

Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#15

Re: Heater Elements

01/31/2013 5:46 PM

AP-1,

Short answer--YES and NO.

Explanation--

  • The cold element, like a non-rotating motor, draws more current than a warm element (or rotating motor). It may take somewhat more time for the element to get to its operating temperature (and lower current draw) than it takes for a motor to get to speed. But, the "inrush" current for the element is much closer to the final current for the element, so the longer time should pose no problem. (This is the YES portion of the answer.)
  • The assumptions inherent in motor overload selection for a given motor application are fairly well-known, with many installation instructions available, so problems can be avoided easily by a competent person. The assumptions inherent in applying a motor overload to a heater are less clear, so errors and accidents would be more likely. You can use trial & error to come up with the proper motor overload selection or setting that would provide steady-state protection against overheating of the element, but I know of no instruction manuals that would apply. (This is a MAYBE portion to the answer.)
  • If the heating element is with a fan to force air past it, and the air flow fails, it is very unlikely that the motor overload would ever sense this problem and provide protection prior to the burning-out of the heating element. Other methods are readily available that can provide such protection, such as a temperature-sensing probe. I know of no codes to which such a use would comply. (This is the NO portion of the answer.)

My overall opinion--don't do this one; it has too many problems and even liabilities.

--JMM

Reply
Reply to Forum Thread 15 comments