Inductive Kick from Transformers

01/30/2013 11:55 PM

I have just familiarized with the notion of inductive kick from inductors due to switching out a path to ground.
However, I am not entirely sure about the effect we would see from transformers because in effect its primarily an inductor. With respect to transformers with the following sequence of events:1) Voltage source connected to primary and load connected on the secondary (i.e. normal operation). 2) Load on secondary is opened or removed (similar setup as an open circuit test for transformers).
Would there be an inductive kick from the transformer causing a voltage spike on the secondary open circuit terminals even though there is some minimal current flowing through the primary terminals? If so, how large of a spike will it be relative to the existing secondary voltage? Will it continue to increase until an arc is formed across the secondary open circuit terminals? Is there a possibility of the core saturating?
My guess is there will be a voltage spike due to the change in current, but I can't be sure since there is a path to ground for the current to flow from the inductor.
Any help on this matter would be much appreciated.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Inductive Kick from Transformers

01/31/2013 3:19 AM

Voltage is the inductance multiplied by the rate of change of current, so, yes, there will be a spike. How large it is depends upon whatever else the transformer is connected to at the instant the current changes and how the change in current is reflected on the primary circuit.

Ground/earth has little relevance, as it only exists to carry fault current in correctly-designed systems and there is no fault in this case.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Jan 2013
Posts: 4
#2
In reply to #1

Re: Inductive Kick from Transformers

01/31/2013 8:43 AM

Thanks for replying. I guess what I am looking for is would the voltage continue to rise until there is a arc across the secondary open circuit terminals. I am thinking of how fluorescent bulbs work with the inductive ballast and the starterswitch.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Inductive Kick from Transformers

01/31/2013 8:50 AM

When one switches anything off that is running on an AC supply, there is usually an arc at the switch. Does that answer the question?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Jan 2013
Posts: 4
#4
In reply to #3

Re: Inductive Kick from Transformers

01/31/2013 10:39 AM

even if the AC supply is cut off only at the secondary of a transformer? Wouldn't the stored energy in the magnetic field be able to release its energy through the primary winding since its connected to a voltage source?

Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#5

Re: Inductive Kick from Transformers

01/31/2013 12:13 PM

The inductive kick is the analog of a water hammer in pneumatic circuits. The faster you stop the flow, the higher is the force to keep it flowing, be it water pressure or voltage.

In water circuits they install small compressible air columns to absorb the kick, in electrical ones, they install capacitors, in both cases, good enough to resist the peak potential.

Remember, with an inductor and a flowing current, you have stored energy and the product stays the same (less circuit losses - resistance etc), so as you try to make current go to zero, the voltage tries to go to infinity, usually something breaks, a spark or ??

__________________
Per Ardua Ad Astra
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#6

Re: Inductive Kick from Transformers

01/31/2013 12:59 PM

Yes there is an inductive kick when the transformer primary is opened and there is no load or a light load on the transformer secondary.

A capacitor across the transformer primary will reduce the voltage kick.
My boss said that if the capacitor current was 1/2 the transformer exciting current the voltage kick would be twice the peak AC voltage.
If the capacitor current was equal to the exciting current, there would not be a voltage kick.

Register to Reply
Participant

Join Date: Jan 2013
Posts: 4
#7
In reply to #6

Re: Inductive Kick from Transformers

01/31/2013 3:07 PM

Sorry, but I was talking about when the transformer secondary is opened and the primary is on a voltage source. Similar to open circuit tests performed on transformers.

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 24
Good Answers: 4
#8
In reply to #7

Re: Inductive Kick from Transformers

02/01/2013 1:26 AM

1. Assuming the voltage source is an AC (50 ro 60Hz) the opening of the secondary side circuit breaker will normally break the current as the current sine wave goes through zero. In which case there will be no voltage spike. If the current is chopped by the circuit breaker as sometimes happens with Vacuum cbs (that is the current goes to zero before the normal sine wave goes through zero) then a voltage spike is probable.

2. Transformers have a shunt impedance (look at the equivalent diagram of a transformer) which will prevent the spike reaching "infinite" voltage.

Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#9

Re: Inductive Kick from Transformers

02/01/2013 8:49 AM

Anytime the flow of current through an inductor (coil) is interrupted, a spark or spike of current will be experienced. This is true for both the secondary and primary sides of your transformer. The generated opposing energy is due to the (L di/dt), where the initial magnitude is normally determined by things such as; initial power applied, frequency of interruptions, number of turns, size of wire used in that particular coil or inductor, etc. Then the energy amplitude will gradually diminish or decay as a factor of your coil's reactances.

__________________
vsar
Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!