Dear Friends, I need to clear exactly wht is diversity factor and y we do that. I Have a example aboutthe diversity factor which i need to explain with one example. I have total load connected for motors is about 745kW and running load is 559kW .then diversity factor is 559/745 = 0.75 is the diversity factor. please can any body tell me what does this mean. I have heard about that diversity effect to cost of power generated at loads and it also says that if diversity is greater than 1 it means low cost . I really want to know after getting 0.75 as the diversity what does this mean. Please i know CR4 is the place where i m not shy to ask but i need to clarify. Thanks sam Reply
Re: why diversiy factor
02/11/2013 5:55 AM
If there are many instances of some type of electrical load connected to an overall system, it may be that not all of the instances will be in use at the same time. Therefore, the electrical system does not need to be as large as all of those loads at once. Diversity factor accounts for this.
In your example, if all the motors were running at once, the load would be 745kw. But since they do not run all at once, the actual load is only 559kw. In the first case, you might need an 800kw genset to handle the load; by accounting for diversity, a 600kw genset might suffice.
Re: Why Diversity Factor?