Induction Motor Starting Current on "NO-Load" and "ON-Load"?

02/21/2013 6:45 AM

Dear All,

(1) I want to know, whether there is any difference between starting current of induction motor on NO-Load" and "ON-Load"??

(2) How to calulate Motor starting current and No-Load Current?

(3) Is there any limit or IS for acceptable value of Motor starting & No-load current with respect to % of FLC or something.

Regards,

T.D.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Ind. Motor Starting Current on NO-Load" and "ON-Load"??

02/21/2013 8:19 AM

(1) Yes, the starting current can be significantly larger than the unloaded current. Why do you think many induction motors have a centrifugal switch connected to starter windings?

(2) I have not bothered to calculate any motor current conditions since I took a motor fundamentals class. There are many additional parameters (core losses, windage, bearing drag, squirrel cage topology and materials, poles, gaps, etc.) that must be known to calculate the motor operation. I prefer to use the motor manufacturer's specifications.

(3) Yes, there is an upper limit to the current that can be driven into any power grid driven device. That limit is usually established by the core saturation of an upstream transformer. The only time this needs to be known is in calculating the arc flash condition. (Same class) For safe usage of a motor, just follow the manufacturer's data in selecting proper circuit protection.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#2

Re: Induction Motor Starting Current on "NO-Load" and "ON-Load"?

02/21/2013 9:31 AM

The induction motor start current does not depend upon load, but the starting duration does. For D.O.L. [direct-on-line] start, the current will be the same as locked rotor current[See NEC Table 430.7(B) Locked-Rotor Indicating Code Letters]

Net acceleration torque for any speed S is Tacc=TM-TL [this would be slight variable and we should state it is constant] where:

TM=motor torque TL=load torque

tstart=wk^2*(ωmax -0)/Tacc/308

TMrat = Php 5,252 / ωmax [rated torque-lbs*ft]

Php=Motor rated power [HP]

ωmax= Motor rated speed [rpm]

If it is NO-LOAD motor start TL (approx..)=0 then Tacc=TM then tstart will be very short.

See also:

Re: Induction motor, inrush current vs locked rotor current

__________________
Julius
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4
In reply to #2

Re: Induction Motor Starting Current on "NO-Load" and "ON-Load"?

02/22/2013 12:50 AM

If no load current is stamped on the nameplate we need not guess it. Similarly the maximum load(inertia)which a motor can start and the time taken to start should be stamped in the nameplate.

__________________
pnaban
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#6
In reply to #4

Re: Induction Motor Starting Current on "NO-Load" and "ON-Load"?

02/22/2013 4:31 AM

I've never seen no-load current on a motor nameplate.

It's not as low as you might expect (20-30% FLC springs to mind, but don't quote me) as the power factor is very low in those conditions.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Induction Motor Starting Current on "NO-Load" and "ON-Load"?

02/21/2013 5:44 PM

Maybe we could help you more if you were to divulge why you are asking these questions.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5

Re: Induction Motor Starting Current on "NO-Load" and "ON-Load"?

02/22/2013 2:52 AM

If we should take Steinmetz Equivalent Circuit and we could establish the Xrotor and Rrotor for a slip=1[slip=(rpmsynchron-rpmactual)/rpmsynchron] for rpmactual=0 at start [see for instance: https://www.selinc.com/WorkArea/DownloadAsset.aspx?id=3690] neglecting Xm and Rfe we could get :

Istart=V/sqrt((Xs+X'r)^2+(Rs+R'r)^2)

As the load is represented here by the slip, as we can see at start the slip is not involved in Istart formula. That means Istart does not depend on load.

__________________
Julius
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #5

Re: Induction Motor Starting Current on "NO-Load" and "ON-Load"?

02/22/2013 5:13 AM

link not working

__________________
pnaban
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#8
In reply to #7

Re: Induction Motor Starting Current on "NO-Load" and "ON-Load"?

02/22/2013 6:44 AM
__________________
Julius
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#9
In reply to #8

Re: Induction Motor Starting Current on "NO-Load" and "ON-Load"?

02/22/2013 9:07 AM

thanks.

__________________
pnaban
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#10

Re: Induction Motor Starting Current on "NO-Load" and "ON-Load"?

03/30/2013 11:35 AM

Dear Mr. tigerdon,

The No Load Current will be 35 to 40 % of FULL LOAD CURRENT but Power Factor will be very LOW to the extent of 0.3 to 0.4.

For other details pl. Refer Standard Text Book of Elec.Engg - INDUCTION MOTOR - CIRCLE DIAGRAM, which will clear all your doubts.

DHAYANANDHAN.S

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (3); Codemaster (1); dhayanandhan (1); JRaef (1); pnaban (3); redfred (1)