Surge Arrester "Low Current" In Pressure Relief.

02/27/2013 12:53 AM

Hi,

Pressure relief current denotes the safe value of current to be vented outside, and this value should be above fault current value. This is high current value.

Can ab please tell me what is 'low current' meaning in "Pressure Relief Current"?

Regs,

sks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Surge Arrester "Low Current" in pressure relief.

02/27/2013 4:16 AM

In what context?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#2

Re: Surge Arrester "Low Current" in pressure relief.

02/27/2013 4:48 AM

I think there's a language problem here. Pressure relief refers to fluids under pressure. Nothing to do with electrical engineering.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3
In reply to #2

Re: Surge Arrester "Low Current" in pressure relief.

02/28/2013 10:04 AM

It has everything to do with electrical engineering of the application of a surge arrester. Gas is a fluid and in this context it is the internal pressure generated as the surge arrester heats up as it is conducting the surge to ground.

From a Selection Guide by GE:

"...In the unlikely case of complete failure of an arrester, a line-ground arc will develop and pressure will build up inside the housing. This pressure will be safely vented to the outside and an external arc will be established provided the fault current is within the pressure relief fault current capability of the arrester. This low-voltage arc maintains equipment protection. Once an arrester has safely vented, it no longer possesses its pressure relief/fault current capability and should be replaced immediately. For a given application, the arrester selected should have a pressure/fault current capability greater than maximum short-circuit current available at the intended arrester location..."

The OP's question is also answered there.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#5
In reply to #3

Re: Surge Arrester "Low Current" in pressure relief.

02/28/2013 10:35 AM

The second sentence is only partly true. There is very little heat or internal pressure generated during normal arrester operation in conducting overvoltage surge current to ground, followed by normal reseal. The buildup of internal pressure and pressure relief is associated with fault current in the event of arrester failure. Arrester failures are typically short circuit so one example in which pressure relief would be critical is circuit breaker or switch close in on a failed arrester.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#6
In reply to #3

Re: Surge Arrester "Low Current" in pressure relief.

02/28/2013 11:02 AM

OK, I thought he was confusing 2 different pieces of kit

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#4

Re: Surge Arrester "Low Current" In Pressure Relief.

02/28/2013 10:18 AM

It depends on the class and construction of the surge arrester but surge arrester standards generally require both high and low current pressure relief tests and ratings for station and intermediate class arresters. Symmetrical rms pressure relief test currents and ratings for station class are typically 40kA - 65kA (high) and 600A (low) and 16.1kA (high) and 600A (low) for intermediate class.

Typical arrester designs will have a two stage pressure relief system to control and prevent the build up of internal pressure. A low current fault may only cause a slight increase in internal pressure, which will initiate a low pressure relief operation, allowing the venting of the excess gas pressure in a safe manner while a high current fault results in a rapid increase in internal pressure which must be rapidly relieved to prevent catastrophic failure of porcelain housings, for example.

Register to Reply