Chilled Water

03/02/2013 12:52 PM

Hi, I am trying to modify a half ton split AC outdoor unit for making chilled water storage of 300L. From 35 degree C to 20 degree C. within a time span of 3hrs.

I have no clue about the volume of evaporator part of this unit.

Please help me how to findout the volume required on the cooling side of the machine to get the optimum out put.

What is the smallest size split unit available in the market, is it possible to get only the out door unitseperately?

Best regards,

Manu.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Chilled water.

03/02/2013 1:19 PM

A 20mm OD copper tube 10m long would be about right. It can be bent or soldered with fittings to fit the shape of the container.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Chilled water.

03/02/2013 1:42 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Chilled water.

03/02/2013 3:12 PM

You have approximately 16,000 BTU/h with this unit. You didn't say anything about re-heating incoming water, so I assume it's a batch process?

Good luck.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#6
In reply to #3

Re: Chilled water.

03/03/2013 6:41 AM

1/2 ton cooling = 12000/2 = 6,000 BTU/h

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #6

Re: Chilled water.

03/03/2013 9:25 AM

Thanks, don't know where 16,000 came from.

Register to Reply
Associate

Join Date: Sep 2010
Location: Dubai
Posts: 38
#4

Re: Chilled Water

03/03/2013 2:03 AM

Your idea is good but you have to consider the following ,.1.the pipe size especially the liquid line ,should not be too big ,to facilitate superheat and expansion.2.the suction pipe should not be too big also.The other issue is the expansion device.If you want to use TXT make sure you use the smallest possible size with adjustible orifice.If you chose to use destributers ,use the smaller capilleries .NB your expansion devise selection can guaratee the lifespan of your compressor and the smooth operation of your chiller ,On the issue of the evaporator,a softdrone copper pipe which is easy to bend by hand ,is ideal,dont use 90 degree elbows use a manual pipebender.

Register to Reply
Member

Join Date: Dec 2008
Posts: 6
#8
In reply to #4

Re: Chilled Water

03/03/2013 12:42 PM

Thanks to all for the advices, to make it more clear I rephrase it as below.

I am cutting off the evaporator / indoor part of a split unit and planning to close it with copper coil and an expansion valve. This copper coill will be dipped in a storage of 300L water to cool that water to 20 degree C.

Another coil is dipped in the same storage tank to heat exchange, that circulates water with incoming temp of 35 degree C. Flow of water in this coil is 100L / H.

Since I am disconnecting the evaporator part from the circuit I wanted to connect same volume of 3/8" copper coil.

No scope to measure the volume physically.

Will it be 50cc approx ?

Hope I am more clear now.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#10
In reply to #8

Re: Chilled Water

03/03/2013 1:26 PM

Why go all that way, cutting and then replacing the existing evaporator with a copper pipe, coiled etc?

You can use the existing evaporator, removing it from the indoor unit and installing it in an enclosing box, pump the water to be cooled through the evaporator directly. You can circulate the water from your 300L tank through this evaporator box, and back into the 300L tank.

Since the existing evaporator is already sized to transfer heat from the AIR, it will still be efficient for water circulating/cooling. Building a new coil as you are planning will be much less efficient at first until you improve it by trial and error...

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Dec 2012
Location: Nigeria
Posts: 23
#11
In reply to #8

Re: Chilled Water

03/03/2013 4:36 PM

Stagnant water cannot effectively exchange heat with running refrigerant. Heat exchange rate is proportional to velosity of liquids. In your case most probably you will find coil freezing unless you are not using a heat exchanger with circulating water

Register to Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#12
In reply to #11

Re: Chilled Water

03/03/2013 9:09 PM

The water needn't be stagnant.

.

As long as the coil adding heat and the evaporator coil are positioned well, there should be plenty of circulation.

.

As long as the evaporator coil allows vertical flow and is positioned in the upper portion of the tank to one side, and the coil adding heat is placed in the lower portion of the other side of the tank, unless the tank is a very awkward shape, or some form of barrier exists, natural circulation will occur.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply
Active Contributor

Join Date: Dec 2012
Location: Nigeria
Posts: 23
#5

Re: Chilled Water

03/03/2013 4:18 AM

After completing the evap coil make sure circulation of water over the coil to avoid freezing

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9

Re: Chilled Water

03/03/2013 12:59 PM

What diameter is the existing suction tube to the compessor?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

From DXB (1); georgerin72 (2); LAA_Lucke (2); lyn (2); SIR G (1); SolarEagle (1); Tornado (2); truth is not a compromise (1)

Previous in Forum: Chiller Protections   Next in Forum: Bucket of Komatsu PC4000-6

Advertisement