What Does 2 * 1500/1 A Current Transformer Mean?

03/03/2013 10:21 PM

I am working in 400kv Switchyard.Here all current transformers are mentioned as 2*1500/1 A rather than 3000/1 A. Now I would like to know why this kind of nomenclature is used.

__________________
Experience is what you got by not having it when you need it
Register to Reply
Pathfinder Tags: ct Current Transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: What does 2 * 1500/1 A Current transformer mean?

03/03/2013 10:33 PM
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: What Does 2 * 1500/1 A Current Transformer Mean?

03/04/2013 2:13 PM

Apart from the obvious answer (it's just two 1500/1A current transformers), are you saying you have a current transformer that is marked 2*1500/1A but is actually for a 3000A primary current?

__________________
jack of all trades
Register to Reply
Active Contributor

Join Date: Aug 2010
Posts: 16
#9
In reply to #2

Re: What Does 2 * 1500/1 A Current Transformer Mean?

03/11/2013 10:26 AM

It is connected to a bus of 3000A

__________________
Experience is what you got by not having it when you need it
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#12
In reply to #9

Re: What Does 2 * 1500/1 A Current Transformer Mean?

03/11/2013 12:36 PM

By the way, 400kV x 3000A x √3 = 2,076 MVA switchward (2 GVA) is this correct?

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: What Does 2 * 1500/1 A Current Transformer Mean?

03/04/2013 2:17 PM

If I saw that on a one-line diagram, I would interpret it simply as 1500:1 CTs on 2 phases.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: What Does 2 * 1500/1 A Current Transformer Mean?

03/04/2013 11:06 PM

What is the rated current of the circuit -1500 or 300A. If 1500A it might mean 2nos CT 1500/5A one for measurement another for protection,if it is single line diagram.

__________________
pnaban
Register to Reply
Active Contributor

Join Date: Aug 2010
Posts: 16
#10
In reply to #4

Re: What Does 2 * 1500/1 A Current Transformer Mean?

03/11/2013 10:30 AM

No, For measurement, different class of CT are used

__________________
Experience is what you got by not having it when you need it
Register to Reply
Associate

Join Date: May 2007
Location: Serbia
Posts: 44
Good Answers: 4
#5

Re: What Does 2 * 1500/1 A Current Transformer Mean?

03/05/2013 3:54 AM

It means that you can make connection (parallel or serial connection) for all current transformers and choose ratio 1500 or 3000 A / 1A .

Good luck

Register to Reply
Associate

Join Date: Jun 2011
Location: ROUEN (in NORMANDY), 120 km from Paris, France, Europe, Earth, Sun Sytem, Milky Way, Universe.
Posts: 39
Good Answers: 3
#6

Re: What Does 2 * 1500/1 A Current Transformer Mean?

03/05/2013 3:59 AM

Hello,

That means you have a C.T. with a double primary winding. If you connect them in parallel you have the double primary current (in your case: 3000 A). This is because your installation has been increased in current, and all switchyard had to be increased in a same way. It is common at conception of a switchyard when it has not been well defined what will be the nominal current, carried by the O.H.Lines. The conception had certainly defined that nominal current would increased at the most five years after starting of the switchyard. And also due to the big price of the 400 kV C.T.'s and their not possible replacement.

Hello, BRZK

__________________
That's all, Folks. Take some time to learn where you live...
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#7
In reply to #6

Re: What Does 2 * 1500/1 A Current Transformer Mean?

03/05/2013 8:18 AM

You meant Double secondary winding !

Register to Reply
Associate

Join Date: May 2007
Location: Serbia
Posts: 44
Good Answers: 4
#8
In reply to #7

Re: What Does 2 * 1500/1 A Current Transformer Mean?

03/11/2013 4:30 AM

No , he thinks double primary winding and the possibility of connection in series or in parallel .

Good luck

Register to Reply
Active Contributor

Join Date: Aug 2010
Posts: 16
#11

Re: What Does 2 * 1500/1 A Current Transformer Mean?

03/11/2013 10:33 AM

Thanks a lot for each and every one of you, for taking trouble in answering questions.

__________________
Experience is what you got by not having it when you need it
Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

brzk (1); dreamchaser (3); jack of all trades (1); JRaef (1); LAA_Lucke (2); lyn (1); Panta SD (2); pnaban (1)