Why Line Matching Units Are Used in Only Two Phases?

03/04/2013 2:17 AM

In 400KV Substation, we have used Line matching unit only on two outer phases(In R & B phases).Line matching unit matches the impedance of line so that High frequency communication signals (e.g. voice signals) can be sent on the same transmission line, which is carrying Power at 50/60 Hz.[Power Line carrier communications]

__________________
Experience is what you got by not having it when you need it
Register to Reply
Pathfinder Tags: LMU PLCC
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Why Line matching unit are used in only two phases ?

03/04/2013 3:16 AM

One of the possibilities is that the communication signals are not sent on the third phase.

The best source of answers is the individual that designed it, though. What does it say on the latest issue of the "as-built" drawings? What does it say in the Control Philosophy document? These cannot be seen from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: Why Line Matching Units Are Used in Only Two Phases?

03/04/2013 12:42 PM

Communications is a two way process. So... one conductor to receive and another to transmit. Hence no need to use the third conductor.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3

Re: Why Line Matching Units Are Used in Only Two Phases?

03/04/2013 2:00 PM

PLCC from one line to ground would probably interfere with other equipment as well as having high loss in the earth return.

Two wires would make a better transmission line. Radiation from lines would be minimised if the two lines carried equal and opposite currents.

The two outer lines are probably symmetrical to ground and the hardware of the lines, making it easy to balance.

However, the third line is probably not symmetrical with the others.

67model

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: Why Line Matching Units Are Used in Only Two Phases?

03/04/2013 5:14 PM

They don't have to be in pairs. PLCC systems can use any combination of phases and/or ground return, it depends upon the overall design philosophy of the communications system, the relative length of the circuit, what type of control and protective relaying is being implemented, simplex vs. duplex, redundacy, separate voice and data channels, higher data rates, age of the system, etc., etc.

From the Westinghouse T&D Handbook, Power Line Carrier Application, page 422, Chapter 36. Methods of Coupling:

"...There are a number of different ways of utilizing one or more conductors of a three-phase power line as conductors for carrier frequency currents... The simplest of these... is to use a single conductor of the power line as one leg of the carrier circuit, with ground as the return path..."

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#5

Re: Why Line Matching Units Are Used in Only Two Phases?

03/04/2013 11:29 PM

All of the above are valid answers. But, the reason is not exactly that. The need for the line matching unit is to carry a relatively low power radio transmission on a differential transmission mode on a pair of wires. It is a very efficient transmission mode.

Equally important is, that a single line works as an antenna without opposing pair. To the neighboorhood its unavoidable radiation decays at r2, that is at the square of the distance from the wire.

In a differential pair most of the transmitted energy is confined between the pair itself, and only the difference of the two radiation reaches the neighborhood. Which is very small compared to a single line transmitter.

Due the low losses, the transmitter needs lower power, the neighborhood experiences much less disturbances.

Register to Reply
Active Contributor

Join Date: Aug 2010
Posts: 16
#6
In reply to #5

Re: Why Line Matching Units Are Used in Only Two Phases?

03/11/2013 10:36 AM

In our national grid,[INDIA], i have found out that Line matching units are always on R and B phases.

__________________
Experience is what you got by not having it when you need it
Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

67model (1); dreamchaser (1); leveles (1); North of 60 (1); PWSlack (1); RAMConsult (1)

Previous in Forum: What Does 2 * 1500/1 A Current Transformer Mean?   Next in Forum: Mixer Grinder Working Principle

Advertisement