Non IS Cable

03/07/2013 9:20 AM

Dear All

Our vendor have lay the non is cable into IS cable is it allowed or do they need to seperated or keep distance to IS cable.

REgard

Moh'd

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: non is cable

03/07/2013 10:34 AM

Provided the required creepage and clearance distances can be maintained, the only thing that would prevent it is the Client's Electrical Installation Standards.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Non IS Cable

03/07/2013 1:42 PM

It depends on the standard you are working to.

For example, I think IEC 60079 (the European standard) calls for 8-10mm separation of cables, 20mm separation of components and 50mm separation of terminations between IS and non-IS but that may change depending on the non-IS wiring voltage.

Consult your local applicable electrical standards for the correct answer.

__________________
jack of all trades
Reply
Member

Join Date: Jan 2013
Posts: 6
#3

Re: Non IS Cable

03/13/2013 8:40 PM

jack right. It is depend on which standard you are working on.

For example, NEC 504 require IS cable to be installed on separated tray, or if installed in the same tray, it will have min 50 mm permanent distance or grounded metal plate separation.

IEC 60079 however call for less requirement. You might place IS and Non IS cable in the same duct/tray provided that the IS cables are having metal sheats or screens.

Also consult the company/client spec requirement

Thanks

Reply
Anonymous Poster #1
#4
In reply to #3

Re: Non IS Cable

03/16/2013 8:51 PM

Dear All

For Non Armoured IS cable lay on cable tray through the metal conduit is it acceptable to standard or need to install separator steel plate.

Any advise

Regard