Motor capacitance to ground check

05/28/2007 2:35 PM

Good day!


Could anyone tell me what minimum value capacitance to ground is considered good when carring out a capacitance to ground test.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#1

Re: Motor capacitance to ground check

05/29/2007 12:41 PM

You need to add some more details to your question.

Motor's single phase power in kW or hp? Or

Winding capacitance
or C in filters in VFD,

or...

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#2

Re: Motor capacitance to ground check

05/29/2007 7:35 PM

I would be surprised if the capacitance to ground be important, I have worked years ago on big AC & DC motors, we were more interested in the value of the insulation to ground and 1 Megohm was considered to be the low end of safe......less than that and we had to fix it!!

I will be very interested to see what other CR4 people will write in answer to your question.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#3
In reply to #2

Re: Motor capacitance to ground check

05/29/2007 9:00 PM

I agree

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Ron Nombri Engineering Fields - Energy Engineering - Ron Nombri Engineering Fields - Power Engineering - Eternal Power Papua New Guinea - Member - Ron Nombri

Join Date: May 2007
Location: Papua New Guinea
Posts: 174
Good Answers: 3
#5
In reply to #2

Re: Motor capacitance to ground check

05/30/2007 1:45 AM

Andy,

I agree with 1 Megaohm, as I use the same concept. Thankyou for mentioning it.

__________________
Kind regards, Ron
Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#7
In reply to #2

Re: Motor capacitance to ground check

05/30/2007 6:29 AM

....less than that and we had to fix it!!

That's easier said than done.

Out of interest, please give a couple of examples from something relatively easy (like drying out a damp motor) to something complex (like a complete rewind).

In your experience what was your best and worst case - what did you have to do 'to fix it['

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8
In reply to #7

Re: Motor capacitance to ground check

05/30/2007 6:51 AM

On DC Motors, it was usually a problem of dirt (carbon dust), remove armature & field windings, clean and re-impregnate the field windings.

Armatures, if defective were replaced and the old one sent back to the manufacturer if cleaning and skimming of the commutator were simply not enough, (an earth to the main shaft for example), but this was rarely the case, it was usually field windings that had earthing problems.....

Usually though it was just a clean and replacement of worn down brushes, new bearings.

On AC motors it was usually just a clean and/or bearing replacement, I remember very few earth problems as the field windings were very well embedded in some green colored stuff, god knows what it was!!

AC motors are in my experience generally much more reliable and require far less "hands on".

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#10
In reply to #8

Re: Motor capacitance to ground check

05/30/2007 7:32 AM

Thanks Andy.

Just as I thought; a lifetime's work summed up in a few words.

Thanks

Cliff.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Ron Nombri Engineering Fields - Energy Engineering - Ron Nombri Engineering Fields - Power Engineering - Eternal Power Papua New Guinea - Member - Ron Nombri

Join Date: May 2007
Location: Papua New Guinea
Posts: 174
Good Answers: 3
#9
In reply to #7

Re: Motor capacitance to ground check

05/30/2007 7:28 AM

Here's a bit of my experience.

Once worked for a cement manufacturing firm on Job Training. We had a lagre induction motor which overheated beyond ambient temperature of 40 °C as we checked with thermal gun, can't remember the actual temperature. The motor tripped several times during previous night shift. Besides that the motor was in operation for quite a number of years. We (2 electricians and I) executed insulation test, found that the motor insulation went below 1 megaohm.

We hired a contractor who rewinded the motor with good insulation. After which we tested, all was O.K. Motor operational temperature was at ambiemt 40-45°C, as with good insulation.

Our induction motor was back on the production line.

__________________
Kind regards, Ron
Register to Reply
Guru
Engineering Fields - Environmental Engineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: May 2007
Location: Anywhere Emperor Palpatine assigns me
Posts: 2774
Good Answers: 101
#4

Re: Motor capacitance to ground check

05/29/2007 11:27 PM

General rule of thumb: not less than 1 Mohm for any resistance to ground.

__________________
If only you knew the power of the Dark Side of the Force
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6

Re: Motor capacitance to ground check

05/30/2007 2:44 AM

It would appear that most of us do not see the need for a capacitance check!

Maybe you misunderstood the need for a high voltage "resistance" check, that is a resistance measurement made with what we called a "Megger" which used a small hand cranked generator to produce a high (could be painfull!) ac voltage, to calculate the resistance of all windings/fields to ground....(I am sure that the equivalent unit today uses batteries and a voltage stepup system!)

Just measuring with a multimeter is not good enough as the voltage used is too low to break down some "illegal" paths to ground!

In the UK, I believe the "Megger" range of instruments were produced by Avo of Dover......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Ron Nombri Engineering Fields - Energy Engineering - Ron Nombri Engineering Fields - Power Engineering - Eternal Power Papua New Guinea - Member - Ron Nombri

Join Date: May 2007
Location: Papua New Guinea
Posts: 174
Good Answers: 3
#11
In reply to #6

Re: Motor capacitance to ground check

05/30/2007 7:46 AM

The equivalent unit today is the Insulation Ohmega Tester.

__________________
Kind regards, Ron
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12

Re: Motor capacitance to ground check

05/30/2007 7:47 AM

In the context of a capacitance-loaded 1/4 wave vertical antenna, as much as possible.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#13
In reply to #12

Re: Motor capacitance to ground check

05/30/2007 9:00 AM

...DUUUH!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.