Can ab please tell me why the neutral of a hydrogenerator shall have full line voltage insulation?

Regards,

sks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Neutral Terminal Insulation for Generator

03/17/2013 3:26 PM

How is the neutral grounded?

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Neutral Terminal Insulation for Generator

03/18/2013 5:18 AM

So that in the event of the neutral-to-ground/earth connection becoming opened for any reason, any consequent line voltage presenting on the neutral conductor will be safely contained and not find its way to ground/earth via inadvertent contact by a person, animal or a spark/arc.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Register to Reply 2 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!

Previous in Forum: What is the Boosting Percentage in Power Rating When an Elevator Will Start to Move   Next in Forum: Danfoss VLT

Advertisement