what happen when the drum level transmitter if the L.P & H.P line is open to atmosphere
how to check turbine vibration sensor and how to fix what is the procedure to fix and measure vibration of the turbine
Re: drum level measurement
03/19/2013 4:15 AM
A1: if the transmitter has been ranged correctly, opening both the HP side and the LP side together will make it read zero.
A2: -
Re: Drum Level Measurement
03/20/2013 1:27 AM
If HP=LP then difference =0.So depending what 0 is set up as , thats what you will read.More than likely 100% or 0%.
Good Answers: 32
03/20/2013 11:50 PM
Hi,
Best way to know open sensor is by detecting no current in 4-20mA look.
For vibrations sensing you need to use Ultrasonic probe with spectrum analyzer or pre tuned probe for known frequency band.
Such things are for experts so ask these questions to your installing expert to answer to you and keep and good manual handy at work.
Shyam
03/26/2013 5:44 AM
If LP & HP open then level shows must be zero, it necessary for boiler protection other wise boiler tube damage & boiler may be explode,(Safety Norms).
For vibration sensor it also depend upon sensor type , if u using eddy current type then fix the gap between the turbine object (like rotor pinion or gear) the output voltage is 10.00 Volts