Can I Use Shunt Release in MCCB

03/20/2013 6:45 AM

Hi friends, I have MCCB model no.-CVS 250F and i want to add shunt release in this MCCB can we use shunt release in that type of MCCB? and what is the exact function of shunt release coil. Regards, Hariom Tomar

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Can I Use Shunt Release in MCCB.

03/20/2013 11:10 AM

Ideally, the topic forms the basis of a telephone discussion with the equipment manufacturer.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2
In reply to #1

Re: Can I Use Shunt Release in MCCB.

03/20/2013 11:31 AM

What is this "telephone" device you speak of?

The Phone Call Is Dead

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #2

Re: Can I Use Shunt Release in MCCB.

03/21/2013 11:36 AM
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Can I Use Shunt Release in MCCB.

03/20/2013 2:41 PM

Ask Schneider, as based on your previous question you don't appear to be electrically qualified to specify or work on a 250A Distribution MCCB.

Don't forget to get someone electrically qualified to install it for you.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#4

Re: Can I Use Shunt Release in MCCB

03/21/2013 11:30 AM

The Shunt Trip (Release) Coil function is to allow mechanical tripping/opening of a Molded Case Circuit Breaker by a remote device other than by the overload & short-circuit mechanism already built into the breaker. (Usually thermally activated)

In many cases the Shunt Trip function is used for Ground Fault protection of the equipment being supplied by the breaker however it can be used to trip/open the breaker for any reason. (Equipment Protection Interlock Permissives, Equipment Safety Permissives, Low Voltage & Over Voltage Protection, Buss Transfer Interlock, and many other reasons as dictated by the application needs.)

Adding a Shunt Trip to a MCCB is a bit tricky and you would be much wiser to purchase a new MCCB that has the shunt trip already included.

Be sure to specify the correct coil voltage rating and the correct auxillary contact configuration needed for your application.

As already stated:

You appear to be lacking in experience and it would be wise for you to contact the selected breaker manufacturer technical support before specifying and/or ordering the breaker and/or shunt trip kit.

If you decide to install a shunt trip kit using in-house personnel:

It is extremely critical to equipment and personnel safety that you test the breaker after assembly following the breaker OEM test procedure to verify correct operation.

This requires a calibrated breaker tester that you can purchase or rent.

Failure to follow this testing can lead to catastrophic equipment failure and/or extreme injury to personnel.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Member

Join Date: Aug 2012
Location: Pune in Maharashtra
Posts: 5
#6
In reply to #4

Re: Can I Use Shunt Release in MCCB

03/21/2013 12:24 PM

Thanks Mr. SHOCKHISCAN, this is really useful to me.

Register to Reply
Power-User

Join Date: Oct 2007
Location: S. California, USA
Posts: 279
Good Answers: 12
#7

Re: Can I Use Shunt Release in MCCB

03/21/2013 1:28 PM

There are several devices that can be used to remotely control a circuit breaker:

Shunt trip device: This device trips or opens the circuit breaker when a voltage is applied to its coil.

Under voltage release device: This device trips or opens the circuit breaker wne a voltage is removed from the its coil. Typically one would select this approach over a shunt trip when there is a need for the circuit to be fail safe.

Remote reset device: With some circuit breakers, one can get a device with motors which can reset the circuit breaker from a remote location.

The reasons one would elect to use such devices are varied. But it starts with a need to turn something off in a hurry. This can be done through monitoring with various devices that connect direct to the circuit breaker, through control logic, or through a switch for an operator to activate.

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers: