Guys I need your technical advise. Regarding Cable Sizing for motor for example I have a cable size of 3C-50+E, I already consider here the current during normal and starting. Current at full load is let say 80A, how to select the MCCB rating? I have read in other books that it suppose to be the current at full load is less than the current of the breaker and this breaker rating should be less than the ampacity of the cable. For example lets say the available size in the market is 130A,is it correct? or is there other data need to consider? Like starting current? My understanding is that no need to consider this because I already consider the starting current during my cable sizing. My idea is to select the nearest higher value to the full load current
Re: MCCB Selection
03/30/2013 9:18 AM
Check EC&M and Mike Holt websites.
pnaban
Re: MCCB Selection
03/30/2013 10:07 AM
Trial and error testing may not be the way to go.
I'd consult NFPA-70 or NEC and not guess.
Of course, a class in electricity would be helpful, too.
Engineering Fields - Electrical Engineering - Ron Nombri Engineering Fields - Energy Engineering - Ron Nombri Engineering Fields - Power Engineering - Eternal Power Papua New Guinea - Member - Ron Nombri
Re: MCCB Selection
03/31/2013 1:27 AM
Hi Nald:
Hope below basic data will assist in some way.
Example: This example is only to illustrate the basic requirements to install the motor. Assuming it is a 45kW or 60.32HP motor at 415V, 80A.
Motor Details:
Kw = 45kW = 60.32HP
FLC = 80A
LRC=263.73
Voltage = 415V
P.F = 0.80
Cable:
Say cable route = 20m
Method of installation = spaced on cable ladder.
Cable Size for short run = 50sqrmm, 3C + E. Cable amps rated at 146A, Ics 7.77kA/s.
35sqmm 3C + E will also be good for the installation, just got protections right.
Motor Starter:
DOL-Direct On Line Starter
Look up NHP Motor Starters and MCCB Catalogues or others for DOLs and MCCBs that will suit your motor.
Voltage Drop:
At 100m, 50sqrmm, 3C + E. Cable amps rated at 120A
Voltage drop is 2.1%, with an allowable voltage drop of 8.7V.
MCCB:
Terasaki MCCB TemBreak 2. Type is S125GJ. (Standard-125A-Meduim-Voltage-Adjustable Settings)
The breaker has adjustable settings which allow you to adjust the MCCB rated amps as required to suit the cable, motor FLC rating, and magnetic trip current settings to be below the cable short circuit rating-so as to protect the cable as well.
For basic motor formulas & calculations, refer to;
http://www.reliance.com/mtr/flaclcmn.htm
http://electriccalcs.com/calculators/view/166/
Refer to previous CR4 links below for more information:
http://www.engineeringtoolbox.com/electrical-motor-calculator-d_832.html
http://cr4.globalspec.com/thread/19925/Motor-Inrush-Current
http://cr4.globalspec.com/thread/34313/How-to-Calculate-Motor-Full-Load-Current
http://cr4.globalspec.com/thread/58774/starting-current-calculation
Kind regards, Ron
Re: MCCB Selection
03/31/2013 3:27 AM
Re: MCCB Selection
04/02/2013 2:12 AM
For over-current protection of a conductor, the Design Current (Ib), should be equal to or less than the MCCB nominal or rated current (In) and In should be equal to or less than the current carrying capacity of the cable (Iz) i.e
Ib </= In
In </=Iz
For short circuit protection, the MCCB breaking capacity should be more than the Prospective Short Circuit Current (PSCC).
However, for motor protection as in your case, the MCCB may be rated at 1.5 to 2.0 times the FL current since the conductor protection is provided by the Over Load protection of the motor. In such a case the MCCB must provide short circuit protection.
Re: MCCB Selection
04/02/2013 6:23 AM
British Standard 7671.