Motor Inrush Current

04/07/2008 12:18 PM

TO ALL....looking for some assistance in calulating inrush current for motors (low voltage and medium voltage). According to some of the literature I am reading, it states to take the full load amps X 6 or 8.

I have not found this data on any of the motor literature I have looked at so far.

Any help would be appreciated.

Thanks

jjbadski

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: El Lago, Texas, USA
Posts: 2639
Good Answers: 65
#1

Re: Motor Inrush Current

04/07/2008 2:27 PM

As a worst case you can take the dc resistance of the wiring in your motor coils.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Motor Inrush Current

04/07/2008 2:43 PM

There is no way to tell for absolute sure on any particular motor without asking the motor manufacturer, because a lot depends upon the construction of the motor itself. There are accepted "rules-of-thumb" which you already cited, but that is about as close as you can get without a lot more information. I suggest you read this paper:

http://www.lmphotonics.com/m_control.htm

Or this one:

http://www.thomasblairpe.com/paper3.pdf

Then pay particular attention to the "AC motor equivalent circuit" section to get a better understanding.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Sep 2007
Location: Reno, NV (USA)
Posts: 608
Good Answers: 66
#3

Re: Motor Inrush Current

04/07/2008 5:58 PM

There is some good data here.

__________________
Aequam memento rebus in arduis servare mentem.
Register to Reply
Power-User

Join Date: Oct 2006
Location: Indonesia
Posts: 102
#4

Re: Motor Inrush Current

04/08/2008 12:07 AM

Inrush current = starting current = lock rotor current =

1000*hp*(kVA/hp)

--------------------

1.732*V

note :

*Where kVA/hp is Locked Rotor Code Letter refer to NEMA table 430-7(b) which is attached on the motor name plate as KVA Code for Siemen's motor.

*This is Approximate calculation only, the result is near 6 to 8 times In.

You may try.

cheers

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#5

Re: Motor Inrush Current

04/08/2008 7:32 AM

The starting current as per IEC or BS should be 6 times the rated current with tolerance .There is a 20% tolerance on Starting current .So maximum can be 7.2 times.Many manufacturers face problems in limiting starting current particularly in 2 pole machines.In such cases the published figure in the catalogue subject to 20% is the max value of starting current.The published values in some cases may be high and when rreferred to rated current may workout to 8 times rated current value.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Anonymous Poster
#6

Re: Motor Inrush Current

04/08/2008 7:47 AM

Look on the nameplate. There you will find a NEMA code (not to be confused with the insulation class) NEMA has established code letters which give you the starting kVA/hp for the motor. Once you have the code letter it is a simple matter to use the appropriate formula. Multiply the hp by the kva/hp factor (since the code gives you a range use the high end value) to get kva then just use basic electrical formulas to get A from kVA (formula depends on motor configuration 3 phase? single phase...) The NEMA standard as I recall is NEMA MG1

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #6

Re: Motor Inrush Current

04/09/2008 11:22 AM

ASSuming he is in North America where NEMA motors apply...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#8
In reply to #7

Re: Motor Inrush Current

04/10/2008 5:55 AM

I have seen motor manufacturer'sdata says its 5.5 some where 6, some where 5 etc.

__________________
BNDas
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#9
In reply to #8

Re: Motor Inrush Current

04/10/2008 10:52 AM

Motor manufacturers will be happy to have 6+20%.Except on 8pole and above without special designs it is difficult and expensive to limit starting current 5.5 PU on 2,4 and 6P

__________________
To avoid crticism do nothing,say nothing,be nothing