220KV Bushing Test Tap is Not Closed During Charging of Transformer

04/03/2013 9:07 PM

Kindly tell me, What will happen if 220KV Bushing Test Tap is not closed during charging of transformer. if any problem of damage will happen to bushing, then why it will happen? what is the technical reason behind it?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: 220KV Bushing Test Tap is not closed during charging of transformer.

04/03/2013 10:34 PM

"what is the technical reason behind it"?

Incompetence!

Register to Reply
Member

Join Date: Sep 2008
Posts: 9
#3
In reply to #1

Re: 220KV Bushing Test Tap is not closed during charging of transformer.

04/04/2013 1:28 PM

Don't say incompetence. You are well knowledge in transformer or power field. But i am working in automation field. that is why i am asking. If don't want to say any answer. please don't comment like this.

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: 220KV Bushing Test Tap is not closed during charging of transformer.

04/04/2013 3:15 AM

Couldn't the transformer manufacturer say, either in the manual or over the telephone?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4

Re: 220KV Bushing Test Tap is Not Closed During Charging of Transformer

04/08/2013 4:01 PM

Several things could happen if the test tap cap is not threaded into place on a HV bushing when energized:

1. The test tap layer(s) of the capacitive paper wrappings of the bushing core could see excessive voltage gradients. Since the cover grounds the test tap point, the test layer could have a voltage across it much higher than it normally sees during testing. Test voltage on a bushing in a Doble insulation power factor test, for example, is seldom over 10kV, while in service the bushing sees 220kV/√3. This could damage the capacitor layer due to "pinholing" or electrical discharge.

2. Dirt, moisture, and contamination could enter the test tap, and possibly contaminate the capacitive layers. This could lead to deterioration of their electrical qualities and cause bushing failure. Water and electricity seldom mix well.

So make sure you put the cap back in place after you finish your bushing tests on the transformer!

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Member

Join Date: Sep 2008
Posts: 9
#5
In reply to #4

Re: 220KV Bushing Test Tap is Not Closed During Charging of Transformer

04/12/2013 12:00 PM

Thank you very much.......

Register to Reply
Anonymous Poster #1
#6

Re: 220KV Bushing Test Tap is Not Closed During Charging of Transformer

08/29/2017 11:15 AM

Hello Muthukumar,

I am quite sure in this case the differential protection relay for 220kV Transformer should trip, seeing one phase harmonics to be missing. Usually a common practice in Siemens, ABB and other reputed manufacturers is to set the harmonics value at 15% with a cross block time of 60 to 100ms.

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers: