Pls explain me the Purpose of testing the short circuit test in transformer.
Thanks in advance
by Sathish
Thanks and Regards, Sathish...
Re: Electrical
04/05/2013 3:09 AM
Re: Electrical
04/05/2013 3:31 AM
To see if it has one, or not.
Re: Electrical
04/05/2013 6:20 AM
The main purpose of short circuit test is to demonstrate the thermal ability and ability to withstand the dynamic effects,Just refer IEC 60076-5.
Re: Electrical Short Circuit Test in Transformer
04/06/2013 7:30 AM
Anonimous 1 gave you the site that explains it for you.
Basically, this test enables you to calculate different characteristics values for the transformer, by just doing this test.
Anonymous Poster #2
04/09/2013 5:45 AM
1st question....do you know how to do the test(short circuit/Impedance test)...if you dont know let me know and I can explain
this test is done to determine if the Transformer will be able to take full load current
...100% of what it is rated and sometimes it is taken up to 130% of full load
Example a 132/22kV Transformer 20MVA:
HV full load current(100%)=20000/132/1.732=87.5Amps
LV full load current(100%)=20000/22/1.732=525Amps
Greetings
Good Answers: 170
04/10/2013 10:21 AM
To know what would be the short circuit current supply capability of the transformer, in real life situations (i.e.) when a worst short circuit occurs at the secondary terminals of the transformer, with rated voltage available at the primary.