Analog PF Meter Connections

04/08/2013 3:02 AM

I have a standard analog meter installed on a generator. The connections were made in way that voltage signal form PT were given at terminals 5 & 8 from phases Y&B (or L2 & L3). Current from R-phase CT given to terminal 3 & out from terminal 1.
However when generator on load the meter does not work with needle tilted downwards at 0.5 PF.

Also I have another digital energy meter on the generator where all readings are perfect & I also confirm that analog meter itself is not faulty.

I think if I change terminals of CT (R phase) on meter such that incoming from 1 & out from 3 the problem might be resolved. I would like to know your opinion on this matter, do you think it will work?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Analog PF meter connections

04/08/2013 3:09 AM

Why not simply try and see?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Sep 2012
Location: Pakistan
Posts: 17
#3
In reply to #1

Re: Analog PF meter connections

04/08/2013 5:22 AM

I want to be sure before I do it :)

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Analog PF meter connections

04/08/2013 5:24 AM

#2↓, or "Nike".

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Analog PF meter connections

04/08/2013 3:17 AM

One of the possibilities is that the meter is giving a true power factor of around 0.5; the forum cannot tell remotely.

What does the manual say? What did the meter manufacturer say in response to the telephone call?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Analog PF Meter Connections

04/08/2013 11:40 AM

We used to be overrun with Naugas around here, but the popularity of Naugahyde in the 60s and 70s resulted in their extincion.

Lerts I feer are on the same path to ruination. Everyone is using a Lert for the siliest things, I even have my iPhone use one 20 or 30 times per day!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#6

Re: Analog PF Meter Connections

04/08/2013 10:48 PM

Let's me be simple basic in principle. You think, your setup produces this. One meter indicates that. Another meter indicates something else.

And you ask us, which one is lying, including your interpretation, as an added possibility.

Make independent measurements. Or better, make independent measurements with personnel, who know what they are doing, certifiably.

Duh.

Ego deflating, and expensive.

You live and learn.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: Analog PF Meter Connections

04/10/2013 9:49 AM

doesn't the meter have a connection diagram lable?

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers: