Time to Exhaust Air from a Known Volume of Containment

04/09/2013 1:40 PM

I would like to calculate the time required to exhaust a fixed volume of air in a container with origanal pressure P, to close to atmoshpheric pressure thru a known cv of a valve.

Are there any Nomograph's available for this?

I would use this in selecting the right size solenoid valve to make a spring return actuaor to close the valve in a required time.

Thanks

__________________
If you don't know where you are going,you are bound to get there
Register to Reply
Pathfinder Tags: exhaust time
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Time to exhaust air from a known volume of containment

04/09/2013 1:47 PM
Register to Reply
Power-User

Join Date: Mar 2008
Location: Houston, Texas
Posts: 101
Good Answers: 6
#2

Re: Time to exhaust air from a known volume of containment

04/09/2013 1:55 PM

I doubt if that is that simple.

You can calculate the instantaneous starting flow but the pressure comes down and so is the outflow.

So the outflow and pressure is is gradually reduced as the pressure in the container is exhausted.

__________________
If you don't know where you are going,you are bound to get there
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #2

Re: Time to exhaust air from a known volume of containment

04/09/2013 2:39 PM

Well,

Nobody here is anxious to do your job for you, even if you knew what information to provide.

Did you even bother to open any of the links?

So long.

Register to Reply
Power-User

Join Date: Mar 2008
Location: Houston, Texas
Posts: 101
Good Answers: 6
#5
In reply to #4

Re: Time to exhaust air from a known volume of containment

04/09/2013 2:44 PM

Yes,

I did

__________________
If you don't know where you are going,you are bound to get there
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #5

Re: Time to exhaust air from a known volume of containment

04/09/2013 2:48 PM

Either measure it or make your calculations at different pressures and average it.

Register to Reply
Power-User
Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - New Member Technical Fields - Technical Writing - New Member Technical Fields - Education - New Member Fans of Old Computers - Apple II -

Join Date: Sep 2011
Location: Bellingham, WA
Posts: 191
Good Answers: 46
#16
In reply to #2

Re: Time to exhaust air from a known volume of containment

04/10/2013 8:01 AM

It's even more complicated than that: the volume of your valve's pneumatic actuator does not remain constant! As pressure is vented from the actuator, the valve stem begins to move. As the piston or diaphragm within the actuator moves, it displaces a different amount of air, thereby altering the equation.

I think this is a case where a real-life experiment would yield the best results. Try venting pressure from the same size of valve actuator through a solenoid, and if the results are unsatisfactory try a different size of solenoid. Attempting to account for all the variables here is fraught with uncertainty.

__________________
They call me "lightning" when wielding a hammer, because I never strike twice in the same place
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#3

Re: Time to exhaust air from a known volume of containment

04/09/2013 2:21 PM

There are not any nomographs available for your application because there are too many dependant variables. Time, Volume, Pressure, Cv.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#7

Re: Time to Exhaust Air from a Known Volume of Containment

04/09/2013 4:12 PM

just a quick question. when you say the word exhaust...are you also using a new source of air to replace the air being moved or are we talking about going into a partial vacuum?

Register to Reply
Power-User

Join Date: Mar 2008
Location: Houston, Texas
Posts: 101
Good Answers: 6
#8
In reply to #7

Re: Time to Exhaust Air from a Known Volume of Containment

04/09/2013 4:28 PM

I am talking about reducing the air presure to atmospheric pressure without inflow of new air.

__________________
If you don't know where you are going,you are bound to get there
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#10
In reply to #8

Re: Time to Exhaust Air from a Known Volume of Containment

04/09/2013 7:12 PM

sounds like a blow-down valve or purge valve any of the manufacturers of this type of valve can tell you, just give them the piping diameter of your exhaust line. or if you have a time element they can suggest sizing. this shouldn't be hard if you're simply exhausting non hazardous air

Register to Reply
4
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#9

Re: Time to Exhaust Air from a Known Volume of Containment

04/09/2013 6:05 PM

Make sure I understand you correctly.....

You want to calculate the time it will take to reduce pressure of a tank to ambient, so that you can use that time to know when to shut the solenoid valve?

I assume the solenoid valve either keeps outside air from entering the tank, or it makes the tank ready for pressurization again....

What is the acceptable range of the pressure of the tank when the valve closes?

.

Here is the thing, I don't know you application, but it seems kind of misguided to attempt to control the process with timing when it seems like pressure is actually what is critical.

Why not close the valve when the pressure is within the desired range?

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply Good Answer (Score 4)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#11

Re: Time to Exhaust Air from a Known Volume of Containment

04/09/2013 9:38 PM

As the pressure decreases, the flow through the valve will decrease as the square root of the decreasing pressure. Thus it is a calculus or differential equation problem, on which I am too rusty. It will behave sort of like half-life in radioactive decay.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#14
In reply to #11

Re: Time to Exhaust Air from a Known Volume of Containment

04/10/2013 4:01 AM

I think that it is similar to the discharge of a capacitor equation.

You need to adapt the values. Anyone keen on this?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12

Re: Time to Exhaust Air from a Known Volume of Containment

04/10/2013 3:56 AM

One wonders why time is so critical for an utility operation such as this. Perhaps the scheme needs putting in front of the local Process Engineer for review and comment before anything is designed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#13

Re: Time to Exhaust Air from a Known Volume of Containment

04/10/2013 3:59 AM

The result depends on the initial pressure since flow laws are function of it. The sqrrt law is valid only within some limits.

A couple of years ago I gave indications for a similar problem in the frame of CR4: it was the time to equalize pressure between two containers. Recently a participant confirmed my results by comparison with results obtained from an other source.

It was not simple work (in fact a system of differential non linear equations with variable coefficients) but the reaction was such a lack of interest that I have not any more the equations and I do not want to do same again for nothing.

As I noticed more and more often theory is not an appreciated skill within CR4.

Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - New Member Technical Fields - Technical Writing - New Member Technical Fields - Education - New Member Fans of Old Computers - Apple II -

Join Date: Sep 2011
Location: Bellingham, WA
Posts: 191
Good Answers: 46
#15
In reply to #13

Re: Time to Exhaust Air from a Known Volume of Containment

04/10/2013 7:58 AM

This fellow's scenario is even more complicated than your example of pressure equalizing between two containers. In your scenario, the containers' volumes were fixed. In this fellow's scenario, the volume of the valve's pneumatic actuator diminishes as the valve stem moves towards the zero-pressure position!

I recommend empirical testing to the OP: get a pneumatically actuated valve, try dumping its air pressure through a solenoid of known size, and then buy a differently-sized solenoid if the time is too long. It's not like solenoid valves are that expensive . . .

__________________
They call me "lightning" when wielding a hammer, because I never strike twice in the same place
Register to Reply
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#18
In reply to #15

Re: Time to Exhaust Air from a Known Volume of Containment

04/10/2013 11:34 AM

I am not sure to understand English very well but as far as my knowledge of this language allows me to get the point the OP mentions a FIXED volume.

I shall have a look at my spectacles may be they are not any more adapted to my view Or am I wrong and this has to be done by others ?

But even if you would be right the problem can be solved also on a theoretical way if of course one knows how to do it.

You know in general when products are designed empirical tests are done in order to verify and the actual trend is to make the so called "virtual prototyping" based on simulation with complex and more and more efficient soft packs.

Register to Reply
Power-User
Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - New Member Technical Fields - Technical Writing - New Member Technical Fields - Education - New Member Fans of Old Computers - Apple II -

Join Date: Sep 2011
Location: Bellingham, WA
Posts: 191
Good Answers: 46
#19
In reply to #18

Re: Time to Exhaust Air from a Known Volume of Containment

04/11/2013 10:30 AM

You are correct that the OP says this is a fixed volume. What I'm trying to communicate is that this assumption is not true. As a pneumatic valve actuator on a spring-return control valve loses pressure, the valve mechanism will begin to move in the spring's "return" direction. This causes the actuator chamber to decrease in volume. Thus, any solution assuming a fixed chamber volume will be incorrect.

__________________
They call me "lightning" when wielding a hammer, because I never strike twice in the same place
Register to Reply
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#20
In reply to #19

Re: Time to Exhaust Air from a Known Volume of Containment

04/11/2013 1:38 PM

I probably misunderstood but what he meant was the time for the fixed container to empty in order to give at right moment the closing command to the valve actuator. It was not considered the whole time.

The actuator behavior was not his concern and thus neither ours.

Register to Reply
Power-User
United States - Member - NE, USA Hobbies - Target Shooting - New Member Engineering Fields - Aerospace Engineering - Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jul 2007
Location: USA
Posts: 199
Good Answers: 6
#17
In reply to #13

Re: Time to Exhaust Air from a Known Volume of Containment

04/10/2013 8:37 AM

Tornado was correct when saying: Differential equations.

Nickname was even clearer: a system of differential non linear equations with variable coefficients.

That would be the right way to calculate it. The calculations would be rigorous, and I am certainly not going to take it on.

Someone else pointed out the obvious as well - if the goal is to achieve a pressure result, contol on pressure, not time.

Register to Reply
Register to Reply 20 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ace Boeringa (1); Fredski (2); JCase (1); LAA_Lucke (1); lyn (3); nick name (3); PWSlack (1); srini (3); tonykuphaldt (3); Tornado (1); truth is not a compromise (1)

Previous in Forum: Comparison Between On/Off Valve and Control Valve   Next in Forum: High Temperature Service - For Controllers

Advertisement