ATS for Commins 250kVA Generator

04/11/2013 7:08 AM

Hi all

we have a cummins generator 250kVA with automatic Transfer switch Part Number 0308-4871-02. There is a problem of automation system. When utility power supply goes off, the generator starts as normal, but it do not stop when the utility power supply returns.

Regards

D.D.Mtonyole

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: ATS FOR COMMINS 250kVA GENERATOR

04/11/2013 7:23 AM

Use the telephone to talk to these people.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Feb 2008
Location: Northeast Ohio, USA
Posts: 267
Good Answers: 9
#2

Re: ATS FOR COMMINS 250kVA GENERATOR

04/11/2013 7:56 AM

Most stand-by generator systems have a "cool down" cycle that lasts 5 to 15 minutes or so. This allows the generator to run in the event there was a very short outage. It is intended to allow the generator to run in those instances so it doesn't start and then immediately shut down. This is adjustable and it probably has a way to defeat it in the event you want to stop the engine before it times out. Have you allowed it to run for a period of time to see if that is the situation?

__________________
All that is necessary for the triumph of evil is for good men to do nothing. - Edmund Burke
Register to Reply
Commentator

Join Date: Dec 2006
Posts: 77
#3
In reply to #2

Re: ATS FOR COMMINS 250kVA GENERATOR

04/12/2013 2:10 AM

Hi

I have allowed enough time to confirm there is something wrong in the change over.

Register to Reply
Power-User

Join Date: Feb 2008
Location: Northeast Ohio, USA
Posts: 267
Good Answers: 9
#4
In reply to #3

Re: ATS FOR COMMINS 250kVA GENERATOR

04/12/2013 7:53 AM

There are various sensors in the panel that could make this happen. One, of course, monitors the incoming power to see if it is 1) - Present; 2) - At the correct phase and voltage; 3) - Sustainable and 4) - Stable. If any of these factors is not suitable, it will not allow the retransfer of the power from the generator to the normal. Usually, there is a small handle that you can use to induce the change in the operation of the system from stand-by emergency power to normal power and vice versa. It may be a small loose rod with a rubber tip. You slip the end of the rod into one of the holes in the rotary transfer mechanism and simply pull it down. This will shut down the system if you move it to the "Off" position, or it can put the system into the "Normal" mode. It should already be in the "Emergency" mode if it is still running. After you put it into the "Normal" position, the generator may continue to run for the cool-down feature I described in my last reply. However, the power should have transfered to the Normal source. If the power is not evident when you put the handle in that position, then it would appear that you still do not have commercial power available, hence the running of the engine. Also, make sure that you have all three legs of the incoming power (for three phase - two legs for single phase). If one leg is out, possibly due to a fuse blown in one leg, the machine will not recognize the power and will stay on the emergency power supply. If you are not sufficiently familiar with this particular ATS, I would suggest that you contact the vendor or the manufacturer for more help. Good luck.

__________________
All that is necessary for the triumph of evil is for good men to do nothing. - Edmund Burke
Register to Reply
Commentator

Join Date: Dec 2006
Posts: 77
#6
In reply to #4

Re: ATS FOR COMMINS 250kVA GENERATOR

04/15/2013 5:53 AM

Thanks When the utility power supply restored, the relays tries to switch to the utility power supply side three times finally it fails and remain in off position (neither utility nor generator connected to the load) and the LED between utility power supply and load starts to brink and the generator do not stop when that alarm exists until reseted.

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#5

Re: ATS for Commins 250kVA Generator

04/12/2013 10:26 AM

Read the manual for the ATS controller. There could be a setting that forces you to perform some command at the controller to restore the system to normal operating conditions (rather than it happening automatically). It may be as simple as that. In some cases an operator may want to have their electricians control the return to normal rather than let the ATS do it.

__________________
To get the right answers, first you need to ask the right questions.