What standard dictates that an undervoltage is defined as voltage <90% of the rated voltage and overload is >105% of the rated voltage?
Re: Undervoltage & overload standard
04/11/2013 9:11 AM
British Standard 7697.
04/11/2013 10:15 AM
The one you obviously don't have, but should.
Get a copy of the standards and read them.
And why do you hide behind a mask of an anonymous poster. What are you afraid of????
Reply Score 1 for Off Topic
Good Answers: 42
Re: Undervoltage & Overload Standard
04/11/2013 10:21 AM
I think the permissible under and over voltage it is referred to the supplied equipment.
For instance, Rotating Equipment Standard IEC 60034-1 Fig.12 states -for frequency from 100 to 102% of rated-1.05 maximum overvoltage 0.95 of rated under-voltage. However, for a limited duration 110% over-voltage and up to 90% [under voltage] it is still permitted.
The overload depends on permissible insulation temperature limits and in turn on ambient temperature.
For cable the permissible maximum load [ampacity] depends on many factors but the limit is the maximum insulation permissible temperature for steady state, emergency or short time.
NEC ARTICLE 100-DEFINITIONS states: "The actual voltage at which a circuit operates can vary from the nominal within a range that permits satisfactory operation of equipment."
Julius
04/11/2013 11:14 AM
Try this.
04/11/2013 2:50 PM
It depends on what part of the world you are referring to as the standards vary. From memory, for Australasia it's AS/NZS 3000.
04/11/2013 3:06 PM
I meant ANSI/IEEE std
04/11/2013 5:13 PM
And the reason a search using keywords can not be carried out at that end in order to find it is what, please?
04/11/2013 5:15 PM
Oh, then I'm not sure as I don't normally have to refer to these series of standards.
Have you tried a quick internet search or a look online at one of the standards store?
04/11/2013 10:25 PM
Undervoltage and overvoltage would be naturally related. Undervoltage and overload are separate categories.
Good Answers: 42
04/12/2013 4:50 AM
For Voltage Levels see:
ANSI C84.1, Voltage Ratings for Electric Power Systems and Equipment (60Hz).
For overload see NEC [Art.430 for motors or 310 for cables or other articles for specific equipment-lighting and so on]
Julius