Current Measurement

04/13/2013 11:13 PM

Hi Team,

I have a doubt in metering circuit please clarify the same.

The current which we observe in a ammeter which is connected to a running motor or oven is inclusion of power factor(power factorised current) or without power factor.

If with Power factor & loss means, i calculate power P=1.732*V*I only

If without Power factor & loss means,i calculate power P=1.732*V*I*0.8

Theoretically i knew the power formula, i need a clear justification that current shown in ammeter when a machine is running is power factorised current(KW current) or KVA current

Register to Reply
Pathfinder Tags: Current measurement
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Current measurement

04/13/2013 11:32 PM

KVA.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Member

Join Date: May 2012
Posts: 6
#2
In reply to #1

Re: Current measurement

04/13/2013 11:42 PM

Can please brief that how to conclude it as a KVA current. Please don't say P=1.732*V*I*0.8

Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #2

Re: Current measurement

04/14/2013 11:49 PM

Because it just IS.

(However, if you have power correction capacitors, you can measure separately the KVA, KVAR, and KW currents, and then compute actual PF.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Current measurement

04/14/2013 12:03 AM

"AC power flow has the three components: real power (also known as active power) (P), measured in watts (W); apparent power (S), measured in volt-amperes (VA); and reactive power (Q), measured in reactive volt-amperes (var).[15]

The power factor is defined as:

.

In the case of a perfectly sinusoidal waveform, P, Q and S can be expressed as vectors that form a vector triangle such that:

If is the phase angle between the current and voltage, then the power factor is equal to the cosine of the angle, , and:

Since the units are consistent, the power factor is by definition a dimensionless number between -1 and 1. When power factor is equal to 0, the energy flow is entirely reactive, and stored energy in the load returns to the source on each cycle. When the power factor is 1, all the energy supplied by the source is consumed by the load. Power factors are usually stated as "leading" or "lagging" to show the sign of the phase angle. Capacitive loads are leading (current leads voltage), and inductive loads are lagging (current lags voltage).

http://en.wikipedia.org/wiki/Power_factor#Definition_and_calculation

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
3
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#4

Re: Current measurement

04/14/2013 1:04 AM

Consider this: Unless your "ammeter" is measuring volts at the same time as amps, then it cannot calculate power factor.

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply Good Answer (Score 3)
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Current measurement

04/14/2013 3:42 AM

An ammeter measures current only and for an ammeter an Amps is an Amps is an Amps. And, that is that.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#6

Re: Current Measurement

04/14/2013 11:39 PM

I spy homework!!

Simple.... amps are measured with an amp meter.... volts with a voltmeter.. the rest you calculate!

__________________
The square root of nothing is what you make it!
Register to Reply
Commentator

Join Date: Nov 2011
Posts: 56
Good Answers: 1
#8

Re: Current Measurement

04/15/2013 7:17 AM

as had been already said ammeters record only ampere readings.if your ammeter is connected before the power factor correcting capacitors than it is the power factorised reading.than to know the power factor you may have to hook up another pf measuring instrument.So now it depends where your ammeter is connected, but anyhow the actual current consumed by the motor is unpower factorised.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#9

Re: Current Measurement

04/15/2013 1:41 PM

Depends on the type of ammeter you are taking/viewing the readings with/on.

If you are using an analog ammeter that is reading directly off the CT circuits or a "hand held" clamped arround the conductor, the readings will be actual current values in Amperes only and the power factor is not visible nor factored into the display.

The KVA calculation formula would be P=1.732*V*I wherein you would substitute the reading(s) taken for the I character in the formula.

This method does not in any way yield the Power Factor of the circuit nor take it into consideration.

Using current readings taken on a oven and applying your second formula that assumes a PF of .8 (P=1.732*V*I*.8PF) would yield a much more accurate result if you are certain the power factor is reasonably close to .8. (Since this would/should be an almost pure resitive load I am pretty sure the PF would be much higher than .8 and most likely >.9.)

Using current readings taken on a motor is quite a different situation as the power factor is directly affected by: mechanical load or abscence of mechanical load on the motor, circuit voltage level, circuit frequency, type of motor (squirrel cage induction, wound rotor, synchronous, VFD, etc.), and if there are motor capacitors present and functioning. Therefore the general practice of assuming a .8PF for a motor may not yield accurate numbers.

All the above being said;

If you are obtaining the current readings from a digital device such as a Motor Protection Relay the power factor may already be taken into account.

In order to determine if the readings are power factor corrected, you must read and understand the meter function and display parameters.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Active Contributor
Engineering Fields - Electrical Engineering - New Member

Join Date: Mar 2013
Location: Papua New Guinea
Posts: 10
#10

Re: Current Measurement

05/03/2013 1:46 AM

The motor is an inductive load, which means it will comprise both active power, kW (for motor rotation) and reactive power, kVAr (to create magnetic field ). The current read therefore will comprise the power factor which is usually labelled on the motor name plate. eg 0.8, 0.85 etc.. That is, I = P/V x pf (for single phase) and I = P/1.732 x V x pf.

For the oven, it is a resistive load, hence it requires only true power and no reactive power. Therefore the power factor will almost be unity. Hence, I = P/V (for single phase) and, I = P/1.732 x V (for three phase)

__________________
"Whatever your mind can concieve, and believe, it can achieve"...Napolean Hill
Register to Reply
Anonymous Poster #1
#11

Re: Current Measurement

05/27/2013 7:29 AM

It is always KVA current except when you running unity power factor ( power factor=1)then KW=KVA

Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

87.saranhp (1); Anonymous Poster (1); brich (1); electricalexpert65 (1); Kilowatt0 (1); nick.mapun (1); pillay (1); SHOCKHISCAN (1); SolarEagle (1); Tornado (2)

Previous in Forum: Servo Controller Design - Software and Hardware   Next in Forum: UPS Problem

Advertisement